J

Jimmyb

Im currently working on a farm yet again :angry_smile: and sorry for yet another question, it just the more i look into things the more i think this cant of been done right in the first place, anyway the service head comes into the barn and then a 50meter cable goto the house which is fused at 60a (even tho its electric hob, cooker and 9.5kw shower in 4 bedroom house rewired in 2003), the size is 16mm, now i thought the design current has to be 60 as thats what its fused at even though i think this should be more and upgraded but anyway this gives a 8.4vd and since this was 16th edition install this only leaves 1.2vd for rest of the circuits, now i realise that some of the circuits are making up the load but surely this cable isnt big enough is it ?

They now they building an extension and want me to quote for wiring and when i mentioned about upgrading the cable i was the only one out of the 4 people quoting that was doing this and my quote was high.

Can someone please help and give me some reason to why im the only one wanting to upgrade to 35mm beside the fact that if i use the 16mm cable at a 50amp design current ive already passed the 6.9vd for lights.

Many thanks for any info

jimmy
 
78 to 94 A is the rating for 16mm SWA depending on method, so current and load isn't your issue. Vd may be, however as you're quite correct that if you calculate the loading at 60A then over 50m you get a vd of 8.4V.

BUT - that's at FULL LOAD. How often do you actually think that the property will be running maxed out? Maybe Christmas morning when the kitchen's at full pelt and Kids are lining up for the shower....even then, do the maths.

A simple way around the Vd problem will be to see what the voltages are at the moment inside the house, and specifically the lighting. If you're OK at the moment on the old cable lengths (which I'd have thought so), then you're only going to improve on that, right?
 
So why is the design current 60A?

i would of thought 60a was reached a quite few time during the day, i thought you had size cable to allow for this or would you just not allow for this ? What design current would you base it on ?
 
Suggets OP reads Table 1B in the OSG (pg 97 in the red one) and works out diversity figures for the design.
 