I'm posting this in here away from the numpties..
So I'm doing various jobs on a house which is to be let out... the client wanting a "satisfactory" EICR when its all done!
1970's house, dual RCD board in place.
One socket circuit covering all the sockets except 1.
Lack of continuity of CPC on socket circuit, cable is 2.5mm /1mm T&E
I've tracked the break in the cable to between 2 sockets .... the client wanted me to leave as is....
The highest Zs on the ring was 1.32 ohms....
Splitting the ring into 2 circuits not viable as the "break" is between a redundant socket (1st on circuit) and the 2nd on the circuit - so placing ALL the sockets on a 20A MCB isn't really an option.
I stated that the faulty cable should be replaced - it not too difficult to run a new cable...
Your thoughts?