I'm posting this in here away from the numpties..

So I'm doing various jobs on a house which is to be let out... the client wanting a "satisfactory" EICR when its all done!

1970's house, dual RCD board in place.

One socket circuit covering all the sockets except 1.

Lack of continuity of CPC on socket circuit, cable is 2.5mm /1mm T&E

I've tracked the break in the cable to between 2 sockets .... the client wanted me to leave as is....

The highest Zs on the ring was 1.32 ohms....

Splitting the ring into 2 circuits not viable as the "break" is between a redundant socket (1st on circuit) and the 2nd on the circuit - so placing ALL the sockets on a 20A MCB isn't really an option.

I stated that the faulty cable should be replaced - it not too difficult to run a new cable...

Your thoughts?
 
Sounds weired that the cpc has gone down inbetween two oitlets without the 2 live conductors being damaged.. are you sure there isnt another outlet or jb where they may have come loose?
 
I'm posting this in here away from the numpties..

So I'm doing various jobs on a house which is to be let out... the client wanting a "satisfactory" EICR when its all done!

1970's house, dual RCD board in place.

One socket circuit covering all the sockets except 1.

Lack of continuity of CPC on socket circuit, cable is 2.5mm /1mm T&E

I've tracked the break in the cable to between 2 sockets .... the client wanted me to leave as is....

The highest Zs on the ring was 1.32 ohms....

Splitting the ring into 2 circuits not viable as the "break" is between a redundant socket (1st on circuit) and the 2nd on the circuit - so placing ALL the sockets on a 20A MCB isn't really an option.

I stated that the faulty cable should be replaced - it not too difficult to run a new cable...

Your thoughts?
Make the installation safe, and don't give him any certs. Write down what you have found, saying that he has refused to have the remedial work done, get him to sign the document,charge him for your time and beat a retreat, although if he is that much of a dipstick, I can't honestly see him paying you anything.
 
Wacking it on a 20A MCB will lead to overload tripping .... on a daily basis IMHO
Maybe so, but it would lead to a satisfactory EICR. If he does start getting tripping due to daily overload after that, it might cause him to act.

I think I'd give him two options for a satisfactory report - fix or reduce the breaker, and explain the implications of both.
 
Firstly, are you sure it is a damaged cable, and not a loose connection in an accessory, e.g. a socket you can't access or locate. I once found such a socket, faceplate removed, L & N connections held together with tape which had stretched and become open circuit over time (earths were twisted, so OK) and then wallpapered over! I had to use a cable tracer kit to find it, then insist I should cut the wall paper to look.

If the cable is damaged, then ideally replace it. A different property, I once found such a cable with broken CPC where a builder moving a partition wall had put a screw right through the cable, severing the CPC and shorting it to L (the flashover residue evidence was there to see, when I got the cable out). Said builder removed the screw, replaced the fuse, and said nothing! I was able to pull the new cable through using the old one. Again, a cable tracer convinced me where the break was first.

Alternatively, is it possible to run a new cable from the CU to the most convenient socket to form a new RFC, and separate off part of the old faulty RFC, e.g. as a circuit on it's own.
 
I agree a 20A will probably cause nuisance tripping, the only option is to replace the cable. Plus fitting a 20A device will make no difference, the fault is still there and you have continuity on the lines and neutrals so you don't actually have an overcurrent issue.
 
I'm 100% sure the break is between 2 sockets... proved beyond doubt... unless the builders have hidden a JB in a plastered wall!
 
lus fitting a 20A device will make no difference, the fault is still there and you have continuity on the lines and neutrals so you don't actually have an overcurrE]

mYmmmMM
I'm 100% sure the break is between 2 sockets... proved beyond doubt... unless the builders have hidden a JB in a plastered wall!
Split the circuit in to 2 radials.?
 
The only issue you have being on a 32A is the worst case fault current on the 1.0 cpc.
 
I'm 100% sure the break is between 2 sockets... proved beyond doubt... unless the builders have hidden a JB in a plastered wall!

Aah yes I found one of those recently as well, and being a builder it was an open choc block in a stud wall ...
 
I could not give a satisfactory EICR with Zs of 1.32 ohms. It is above the rule of thumb, just! I would advise the client of this and insist repairs are made to meet BS7671. I know it is a very marginal thing but if something goes wrong someone will be knocking on your door! I do like the idea of two radials though.
 