So exactly how hard will it be to replace the faulty cable - is this something fairly straightforward that the customer is just too mean to pay for, or will it be time consuming and costly?
 
It is the only solution down rating the mcb does not remove the issue.
 
If there is enough of a profit margin in the EICR and easy to replace the cable I would just do it.
Why?, I understand if the client is a regular and all that , but even so I think the OP has done more than his fair share, to spend time locating the fault.Not part of the report IMO, you will all be working for nothing.?
 
I don't do these EICR things, but found loads of 'faults' doing new work. Told the customer, who can't be arsed to do anything about it. So now I just note on the cert', and try to get a good night sleep, quite hard as I get older! :)
 
I would split it into two radials even though all the sockets bar one will be on one of the circuits. Explain to the client the likely hood of the breaker tripping due to overload but are doing this so they can have their satisfactory EICR and wont be held responsible for any issues if and when it does trip as you've told them the best solution is to replace the knackered leg of the RFC.
 
hardly a sensible split!
Was not thinking of a stupid split was thinking upstairs and downstairs being the two radials. What was you thinking...sigh:rolleyes: But probably more trouble than replacing defective cable, so back to the drawing board
 