Never changed a DB on a TT system before, question is if all final circuits will have 30ma RCBO devices what (if required) RCD will I need to install on the meter tails supplying the DB.

The rod currently with the Earth to MET disconnected reads a healthy ze- 98ohms which is quite good for a TT, with earthing conductor connected parallel with paths give me 0.22zdb.
 
Last edited:
if using an rcbo ccu you just need to use a compression gland to hold the tails as they enter the board, if you are using a dual rccb you need to swap the main switch for a 100ma s type, and again use a gland...

the amount I'm coming across lately that have been change and neither of these things done is scary!
 