Got asked to look at a job, for a lad i used to work with in the security side of life. Actually it was his sisters house . So like anything else you put it off because you can. He said the shower cct kept tripping. He said it was other earths causing it and ditched them in the CU (horror) hence my visit tonight not next week.

Gets to the job, striaght into board, then earthing. Then sit down, then check again. Meter out ELI check, Any way see photos below, sorry one is slightly blurred but that wasnt my concern at present.
IMG_0289.jpg
IMG_0290.jpg

We wonder why the yellow test button doesnt work lol, (does now after some tweeking)
No main earth, no gas bond, water bond 4mm.
Switch off 2 breakers to isolate the RMF.
I have rings inside of rings with earth faults all over.

Well before i could do anything else i needed to make safe first.

Need to clear my head now lmao
 
Tell them your now a plumber.

I like a chalange.. Ill sort for free..


However I don't work in houses that post codes start in NE
 
Yer Its a box of frogs, Normally before i change a board i do all my testing, but in this case,,,,,lol

Before i left Ze at 0.13ohms, voelcb now works lol, Managed to lash a bond onto gas and water, not at correct point , but i got it on at least sort later. Ditched the shower cable, because that kept popping mcb, didnt have time to R1/R2 it and check insulation.

@ bigbaddave , like chalenges too, so let the battle commence, this is why i love being a spark, always something new to play with.

Down side slightly reduced rates but i will still get my beer tokens out of it.
 