No.
You need to check the R1 and R2 on this spur, but this spur will be short, so will give untypically low figures for R1+R2. You need to record the highest R1+R2 for the circuit, which will be somewhere near the middle if it's a ring, or at the extreme end if a radial, or possibly at the end of a long spur off the ring.
If it's a complete ring, the R1+R2 should be the same throughout the circuit, surely.
 
If you measure R1 and R2 (or R1+R2) directly at various points on a ring, rather than by doing the figure of eight test, the maximum figure (which is the one to record) should be found at the socket outlet "furthest" from the origin, ie about half way round the ring.

R1+R2 is the result gained via the figure of eight test and should be equal at each point of the rfc.
 
R1+R2 is the result gained via the figure of eight test and should be equal at each point of the rfc.

Yes, I understand that, but are you saying that it is not permitted to measure it directly, like on a radial circuit? ie do you HAVE to use the figure of eight method?
 
Yes, I understand that, but are you saying that it is not permitted to measure it directly, like on a radial circuit? ie do you HAVE to use the figure of eight method?

If you want to get your R1+R2 figure then you can use the figure of 8 method
or you could add r1 to r2 and divide by 4.
The figure of 8 test (as detailed in the OSG) if the recommended method because you can check R1+R2 at each point and check polarity (also as detailed in the OSG).
 

Reply to which is the besst way? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
894
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
773
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
708
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
624
Hi all, Curious one and hopefully some one of you could give me some advice. A customer has had a steeltech shed installed at their premises. A...
Replies
17
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock