I'd just record the Zs in that example, in reality that would almost always be a low cost job and you wouldn't be allowing the time for end to end testing.
Do you not confirm that the ring is actually a ring and that adding a extra socket brings a final of overloading part of the circuit as it's discontinuous?
I record it just to cover my self really
 
Generally the Zs reading would tell you a lot about that Ian but I'd check both ends were live at the point I was taking the spur from while disconnected.
 
Do you not confirm that the ring is actually a ring and that adding a extra socket brings a final of overloading part of the circuit as it's discontinuous?
I record it just to cover my self really
If I work on a ring final I always note the continuity readings.
 
Generally the Zs reading would tell you a lot about that Ian but I'd check both ends were live at the point I was taking the spur from while disconnected.
What disconnect the ring, liven it up and see if both ends show voltage.
 
As a side note do any people write down the ring continuity results if say spuring a double socket from local ring final circuit in the comments section?

I record continuity readings in notes in MW. In fact I test for such before starting my addition. Always have my fingers crossed when doing so, you never know whether the DIY'er been there before you :)

Edit; That said, never checked the RFC if spurred from the origin at the CU.
 
Last edited:
I record continuity readings in notes in MW. In fact I test for such before starting my addition. Always have my fingers crossed when doing so, you never know whether the DIY'er been there before you :)
Yes I know that feeling
 

OFFICIAL SPONSORS

Back
Top