Customer had been having problems with their downstairs living room lights and up stairs hallway lights since they moved in.

Downstairs light was switched by 3 switches and the upstairs by 2. A 2 gang switch downstairs, 2 gang switch upstairs and intermediate downstairs.

The switches were mechanically sound, but depending on which order you switched them on or off they may or may not switch the light on or off, so customer was running back and forth between switches to get the light on of off.

In other words the conductors were not were they should be!

I could not figure it out whilst with the customer, so went home and drew my diagrams and eventually worked it out and fixed it. Took me about an hour of thinking and scratching my head and it felt great when eventually the diagram worked!

No neutral conductors in switches (all either PL or SL), only did a quick test in one of the switches and found a P/L as shown in diagram, cables drawn going in random direction as had to work that out myself (so so do you :smile5:), no junction boxes elsewhere. Haven't drawn any earths.

I realise its pretty sad but I get a bit excited about these sort of things and I thought I might get away with just a small amount of stick by posting here!!! I realise this may be simple stuff for most but I reckon it'll still make you think for a while. Anyone good at drawing diagrams and going to have a shot at the answer? :smilewinkgrin:

View attachment Light Problem.pdf
 
On a quick review without writing it out and probably wrong but swap yellow and black in the middle switch.

Edit: and swap blue and black at the top left switch.
 
Last edited:
Customer had been having problems with their downstairs living room lights and up stairs hallway lights since they moved in.

Downstairs light was switched by 3 switches and the upstairs by 2. A 2 gang switch downstairs, 2 gang switch upstairs and intermediate downstairs.

The switches were mechanically sound, but depending on which order you switched them on or off they may or may not switch the light on or off, so customer was running back and forth between switches to get the light on of off.

In other words the conductors were not were they should be!

I could not figure it out whilst with the customer, so went home and drew my diagrams and eventually worked it out and fixed it. Took me about an hour of thinking and scratching my head and it felt great when eventually the diagram worked!

No neutral conductors in switches (all either PL or SL), only did a quick test in one of the switches and found a P/L as shown in diagram, cables drawn going in random direction as had to work that out myself (so so do you :smile5:), no junction boxes elsewhere. Haven't drawn any earths.

I realise its pretty sad but I get a bit excited about these sort of things and I thought I might get away with just a small amount of stick by posting here!!! I realise this may be simple stuff for most but I reckon it'll still make you think for a while. Anyone good at drawing diagrams and going to have a shot at the answer? :smilewinkgrin:

View attachment 21373
yeah..it is..

have you heard of a wander lead and a low resistance ohmmeter eh?
 
A quick (late Saturday night) punt:

middle accessory in your diagram is the culprit. On the downstairs light switch, the red single core should be on common, the t&e should be on NO and NC. The 3 core should just be for the upstairs light switch on the right: yellow and blue on NO/NC, PL (red) on C.
 
Having now thought about it each light switch is using a standard two core two way switching arrangement, the three core between upstairs and downstairs two gang switches is also taking the PL down to the downstairs switch on the red core.

Downstairs switching:
black single core may be permanent line to downstairs switching (since red single core not identified as PL), red single core switched line to downstairs light.
twin and earth from downstairs light switch to intermediate to upstairs light switch.
Should be L1 and L2 for red and black (on T&E), common for single cores.

Upstairs lighting:
Permanent line (red) in connector and switched line (black) (in common) from upstairs light fitting in T&E
Three core cable takes PL down to downstairs switch(why?) , (red core) should be on common.
Blue and yellow should be in L1 and L2 for the upstairs light switches (up and down).
 
Reasoning: PL for upstairs supplied on red t&e in the top left of your diagram, the black of that cable is the SL for the upstairs light. The yellow and blue are strappers. For downstairs, PL comes in on the single black (to C, top right), the t&e goes to the intermediate, the other t&e from the intermediate should go to NC and NO of your middle switch, and the single red goes to the light (SL).
 
As you don't say which lights are not functioning,if both arriving sets of strappers at intermediate switch have same colour conductor swopped will cause same issue,eg strapped swiches functioning ok in one intermediate switch position and not functioning in the other. Now i'm going to give this cylinder another spin and pull the trigger again.....
 
As you don't say which lights are not functioning,if both arriving sets of strappers at intermediate switch have same colour conductor swopped will cause same issue,eg strapped swiches functioning ok in one intermediate switch position and not functioning in the other. Now i'm going to give this cylinder another spin and pull the trigger again.....

My very first thought.......at this time, on a sunday morning.:!blank:
 
A quick (late Saturday night) punt:

middle accessory in your diagram is the culprit. On the downstairs light switch, the red single core should be on common, the t&e should be on NO and NC. The 3 core should just be for the upstairs light switch on the right: yellow and blue on NO/NC, PL (red) on C.


Having now thought about it each light switch is using a standard two core two way switching arrangement, the three core between upstairs and downstairs two gang switches is also taking the PL down to the downstairs switch on the red core.

Downstairs switching:
black single core may be permanent line to downstairs switching (since red single core not identified as PL), red single core switched line to downstairs light.
twin and earth from downstairs light switch to intermediate to upstairs light switch.
Should be L1 and L2 for red and black (on T&E), common for single cores.

Upstairs lighting:
Permanent line (red) in connector and switched line (black) (in common) from upstairs light fitting in T&E
Three core cable takes PL down to downstairs switch(why?) , (red core) should be on common.
Blue and yellow should be in L1 and L2 for the upstairs light switches (up and down).

Happy Steve beats Richard by a whisker!! :smiley2: And beats me by about a whole cat!!

Have to admit I thought the single red core was PL for DS light and single black core was SL for DS light (this would work) but then (as Steve says) you wouldn't have needed the choc block so it must be the other way around as there is a choc bloc!

View attachment Faulty set up.pdf

View attachment Solution.pdf
 
Mornin'! :-)

Thanks for posting this question, happyhippydad. I come on this forum to learn (and a little bit for the banter). Questions like this are always appreciated, make you think. Hopefully, when I start my training, there'll be more like this.

My understanding is that you still don't need the chock block, if you did want to eliminate it. In your solution:
- move black from upper light fitting t&e from top uplight C to join the blue one (say) NC.
- move red from upper light fitting t&e from chock block to join the yellow one NO.
- move the other red (from 3 core), currently in chock block, to C.
- bin chock block.

As a final flourish, if in the middle accessory blue is on NO and yellow is on NC, then swap them round on the top accessory (blue on NC, yellow on NO).

Sorry if this is egg-sucking stuff, last thing I want to do is put anyone's nose out of joint... as I say, very much on the "still learning" side, so if what I'm saying's too trivial, or just wrong, just set me straight.

Cheers :-)
 
Mornin'! :-)

Thanks for posting this question, happyhippydad. I come on this forum to learn (and a little bit for the banter). Questions like this are always appreciated, make you think. Hopefully, when I start my training, there'll be more like this.

My understanding is that you still don't need the chock block, if you did want to eliminate it. In your solution:
- move black from upper light fitting t&e from top uplight C to join the blue one (say) NC.
- move red from upper light fitting t&e from chock block to join the yellow one NO.
- move the other red (from 3 core), currently in chock block, to C.
- bin chock block
.

As a final flourish, if in the middle accessory blue is on NO and yellow is on NC, then swap them round on the top accessory (blue on NC, yellow on NO).

Sorry if this is egg-sucking stuff, last thing I want to do is put anyone's nose out of joint... as I say, very much on the "still learning" side, so if what I'm saying's too trivial, or just wrong, just set me straight.

Cheers :-)

Very nicely done HappySteve! Whenever I have fitted 2 way switching (not often as still very inexperienced) I have always fitted as you have just explained above and I was thrown a bit by this set up. I hadn't noticed you could just revert back to the 'normal' way of doing it.

You do make electrics sound glamorous :smile5:
 