putting it simply, there are 3 commonly used earthing systems over here.Dave I can’t thank you enough that’s been bothering me. I’m here to learn and was starting to feel like an ldiot. I’m not educated like y’all I had to quit school in the 9th grade to get a job to help my mom since I didn’t have a dad. I am not the best electrician out there but I’m not the worst either. I’m sorry if I made you mad. Please don’t have no hard feelings I don’t want to be kicked off this forum. It seems like I cause more trouble than anybody
1. TT. this is where earth rod/s are installed at each installation. this is the responsibility of the home owner to employ an electrician to install.
2. TN-S. here the incoming cable is lead sheathed and buried underground. a sweated or clamped connection is made at the customer's property, by the network operator (who is responsible for the earthing arrangement up to this point). electrician then connects the installation earth to this. the lead sheath of the cable is then the earth. not used on new installations as current supply cables are not metallic sheathed.
3. TNC-S. here the neutral is connected to the installation earth, again by the network operator. the supply cable has the N spiked into ground at intervals.