Im waiting for acceptance in the training forums but whilst I do I have a question. Ive always been told to earth things for example sockets that are not standard plastic but shinny nickel, I know you can get away with just using the lugs on a back box and the screws which are used to pull the socket face plate tight to the metal back box if the lugs are fixed however I still but an earth cable from the earth terminal on this back box to the earth terminal on the back of the socket juse because its good practice imo.

Whats baffling me is these new spotlights Ive just got from screwfix, they are Robus and the instructions say DO NOT EARTH! my initial thoughts were that this was a mistake but upon further investigation there is no earth terminal at te fitting just a Live and Neutral. My question is why dont the have an earth terminal as surely this is wrong. They are chrome so surely an earth is needed. Tempted to ring Rombus up and ask why but thought I would try here first as one of you guys will probably no why?

cheers
 
are these GU10 fittings? the answer is that the lamp holder is electrically separate from the metal housing and as such they are classII items. earthing is not required.
 
The appliance will usually be double insulated and will have a symbol on it that looks like a square in a square. This means that any metal in the fitting is protected from contact with the supply and does not need to be considered as an electrically conductive part in this instance and therefore does not required bonding via the CPC to the main mass of earth.
 
Class II mate.

Have a look on google at class I and class II items.

Do the instructions or box have a square with a smaller square inside?
 
Cheers guys I wondered what was going on for a moment there but yes they have a square within a square symbol so are double insulated (just learnt something) with additional safety precautions such as supplementary insulation taking place.

Im obviously using 1.5mm twin and earth to wire these in and at work I always put the earth into a choc block if the alternative is to cut it of. From what Ive just read on google and picked up on here it really isn't needed?

If it was you would you just cut the cpc's of or should I just choc block them for good pactice.

cheers again

Justin
 
Cheers guys I wondered what was going on for a moment there but yes they have a square within a square symbol and Ive just learnt that that means itit has additional safety precautions such as supplementary insulation. Im obviously using 1.5mm twin and earth at work I always put the earth into a choc block if the alternative is to cut it of. But from what Ive just read and picked up from here it really isnt needed. If it was you would you just cut the cpc's of or should I just choc block them for good pactice. cheers again
Good practice would be to choc block and tape. If the customer replaces the fitting at a later date then the next electrician will appreciate your consideration as he may require the CPC if the new fitting is class 1.
 
aarrrrgggggh. choc blocks. use bloody line lighting kits. T/E into the line enclosure one end. flex out to fitting. terminate the cpc inside the line enclosure.
 
One method would be to use a JB(not a round one)and terminate into it and take suitable flex to each downlight.
 
nothing wrong with round JBs either. they are accessible through the hole in the ceiling. just fiddly.
 
anything worng with 30A terminal heavy junction box for this job as ive got a couple in the van
 
cheers I just like to double check everything it in my natre. right of to do the spotlights now thanks for the help :-)
 
What wattage are these lamps that they need 1.5mm² conductors and 30A terminal blocks?

Sorry, just pet hates.
 