I

irishsailor

Dear All

Newbie here, I was wondering how to go about wiring a garage. I mean conncting into consumer unit from the house. I am happy with burying SWA and using caterary wires.

How do u go about connecting in to the house CU?? The garage will be required to have a lighting circuit and a power circuit.

Do u need separate circuit breakers, or can you fuse spur off for lighting??

Irish
 
i would go from house CU into a Metcad DP switch. teminate end of SWA in there and also provides DP isolation for garage and submain. would prefer to do this on Non RCD side.

then take SWA directly into garage unit (RCD main switch, and MCBS dependant on what you need, normally 16A/20A and a 6A). depends on your requirements

by havin and RCD in garage rather than house, if your lawnmower etc... trips the RCD your not trailing mud in house resseting it.
 
But surely the armoured cable has to also be protected by rcd??

Hey mate.

If the armoured cable is installed on the surface which usually the are, then there is no requirement to RCD protect it.

Same as if you install a circuit for a fridge or a freezer on the surface in trunking/conduit and label it for it's use then this too can be non-RCD protected.

Cheers.:D
 
Hey mate.

If the armoured cable is installed on the surface which usually the are, then there is no requirement to RCD protect it.

Same as if you install a circuit for a fridge or a freezer on the surface in trunking/conduit and label it for it's use then this too can be non-RCD protected.

Cheers.:D


If the Armour is earthed you can sink SWA into plaster without putting though an RCD
 
Last edited by a moderator:

Reply to Wiring a Garage in the Australia area at ElectriciansForums.net

Similar Threads

I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
708
Hi all hope u all have a fab christmas , my name is Nick and i bought a roller garage door it got delivered yesterday but due to holidays the...
Replies
0
Views
545
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
I have a detached garage with a 60 AMP subpanel which has lost power. I traced the failure to the wire running under the walkway via conduit...
Replies
3
Views
761
can anyone please advise on where the wires go? My electrician installed a new cable ready for when I bought a security light. The cable as shown...
Replies
3
Views
527

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock