Hi all, newbie here with an opening post/problem

I've just acquired a metal lathe, and to cut a long story sideways I've been having problems wiring the motor to a switch box. The FLA reading on the motor says 3.75, so I bought a switch box with an overload amp rating of 2.5-4 amps (assuming that would be good for the motor). When I plug the motor directly into the socket, there's no problem with the fusebox in the garage (where it's set up), however when I wired it up to a switch box, it's constantly tripping the RCD.

So basically my question really is - where the hell am I going wrong?

ANY advice/ideas/insight on the matter would be massively appreciated, any details just ask.

Ta
Dom
 
You need to give more details. Voltage, single phase or three phase? Connections etc.
What is the supply voltage? Some photographs would help.
 
ok, this should be everything:

supply voltage is a normal 240v socket

(on the motor)
220-240 volts
single phase
3.54 (sorry not 3.75) F.L. Amps
0.5 HP
Class E (I don't know if this is relevant)

(switch/starter)
DOL Single Phase Motor Starter c/w Overload of Choice

2.5-4 Amp overload
240 V contractor coil

here are some pics of the motor, inside the starter and inside the starter housing.

motor.jpg
switchbox.jpg
switchbox_housing.jpg
 
Last edited by a moderator:
Cant really make out how you have wired that? There is a red in L1 and brown in L2?
 
thanks a million Tony, I'll give it a whirl and report back tomorrow if there are any problems
 
You need current flowing through all 3 contacts as per Tony's diagram, otherwise the O/L will see an imbalance and trip.

However, you say that it is tripping an RCD in a switch box? but not on the garage fuseboard. Please explain in more detail how your supply is set up.
 
You need current flowing through all 3 contacts as per Tony's diagram, otherwise the O/L will see an imbalance and trip.

However, you say that it is tripping an RCD in a switch box? but not on the garage fuseboard. Please explain in more detail how your supply is set up.

I have a separate fusebox for the garage. Basically the house has a main fusebox (standard), but a separate wire runs out of the fusebox into a secondary fusebox for the garage since it's detached from the house. I think (I'm not pro, I've just worked this out for myself) that maybe it's drawing too much power? The motor is fine when plugged into a normal socket, it's just when I wire it to the switch/starter that it trips the RCD in the garage and thus the main switch in the house.
 
If the motor runs fine when plugged in to a socket then there's a good chance it's you wiring of the DOL starter.

It might be worth a quick IR test of the windings, if they're okay (>2Mohms) then wire up as per Tony's diagram.
 