What do you guys write under the following on your EICR forms
1. Extend of the electrical installation covered by this report What it says. If the EICR covers the entire installation then state that, if it only covers the house and not the garage state that
2. Agreeded limitations This is limitations agreed with the client. Technically you would discuss the extent of testing and inspection with the client prior to work commencing. If the client decides they want to save money by omitting the R1+R2 test that would be an agreed limitation.
3. Operational limitations This would be (for example) where access to a part of the installation was not possible at the time of the inspection, perhaps because of a safety issue if the correct access equipment was not available. This would be stated in this section
Cheers
[automerge]1591294257[/automerge]
In a domestic property