Have you done an IR test now and compared it to your EICR from when you fitted it? Also do a continuity test in-between both neutral bars just in case someone has tapped into a circuit since installed.
 
well if all things being equal , and no changes to the wiring.............

then the shower is still faulty no matter how many elements the repairman replaces.
;-)
 
Yeah , its the shower that's faulty no doubt , but it should be tripping its own rcd not the other one and staying on
 
This is a real vague shot in the dark...!!!!!!
Is the shower cable running tight alongside another connected to the other side of the board and inducing a current in that cable's Neutral???
Have you tried clamping each circuits Neutrals on the tripping side, when the shower is on max?


Clutching at straws here!
 
Ill try that , I went today for 20mins to double check my work basically to rule out it being my fault , although its been fine for 6 months so obviously a new fault but wanted to show face
 
Showers have two heating elements, when the second element kicks in that is when it trips so that is the fault. Check the internal connections of the shower before sending it back to the wholesalers.
 
I had a 16th ed board, where the lights were not protected by an RCD, but if you turned the lights on off quickly it tripped the RCD in the board (even tho they weren't connected to it).
Swapped the RCD (even tho it seemed ok)
Problem solved

i would try changing the RCD
 
We didn't supply the new shower only rewired , customer didn't want to change it , Triton guy been out to replace element

- - - Updated - - -

Did you find out why that happens
 
I had a 16th ed board, where the lights were not protected by an RCD, but if you turned the lights on off quickly it tripped the RCD in the board (even tho they weren't connected to it).
Swapped the RCD (even tho it seemed ok)
Problem solved

i would try changing the RCD

did you find out why that happend

- - - Updated - - -

The second element ?
 
I would check the offending rcd. It sounds to me that either the two poles are not making properly when switched on or a loose connection maybe on the ingoing side.
 
I would check the offending rcd. It sounds to me that either the two poles are not making properly when switched on or a loose connection maybe on the ingoing side.

Even if its totally fine until shower switched on to high though
 