Could be spikes from the electronic control causing currents to flow through capacitive filters on for example a washing machine. Have they got a new washing machine etc recently. Best way to test this is to unplug all the appliances and see if fault goes away. Just disconnecting the live doesn't work as they have capacitors N-E too and there could be spikes on the neutral too. had this problem once where spikes from church SON lamps tripped RCD in adjacent house.....Hope this helps
 
I've come across a very similar fault, someone had done a board change and everything worked. Now and again, when the Rcd tripped it would trip both or only one, with a full test I found both ring mains interconnected across both rcds. Main reason I was called to site was because when an Rcd needed resetting you had to turn each CB off and both rcds. The install actually functioned fine most of the time, albeit not very safely.

In my 22 years experience I've found 95% of the time, the simplest and most obvious answer is usually the right one. I'd start with checking continuity between the 2 neutral bars with CBs off then with them on, with power off of course.
 
[FONT=&amp]This thread reminds me of a Sherlock Holmes quote,”When you have eliminated the impossible, whatever remains, however improbable, must be the truth?”[/FONT]

[FONT=&amp]Here are a few things to think about.[/FONT]

[FONT=&amp]a) Has anybody else worked on the consumer within the six months?[/FONT] [FONT=&amp]
b) If you perform an RCD test, does the RCD’s correspond with the circuits tested?[/FONT]
[FONT=&amp]c) Is the second RCD feed from the first RCD (non time delay)?[/FONT] [FONT=&amp]

I know they are long shots, but at least we can eliminate them from the list.[/FONT]
 