I've come across a very similar fault, someone had done a board change and everything worked. Now and again, when the Rcd tripped it would trip both or only one, with a full test I found both ring mains interconnected across both rcds. Main reason I was called to site was because when an Rcd needed resetting you had to turn each CB off and both rcds. The install actually functioned fine most of the time, albeit not very safely.
In my 22 years experience I've found 95% of the time, the simplest and most obvious answer is usually the right one. I'd start with checking continuity between the 2 neutral bars with CBs off then with them on, with power off of course.