glasgospark

6 months ago we installed dual rcd db and rewired shower circuit .
Customer contacted me to say shower is tripping rcd, Triton changed element still doing same so I go up , shower works fine on medium at temp 10 but trips rcd when put to high , when it trips its tripping the other rcd and shower stays on .
so rcd that trips doesn't have shower circuit on it but when shower turned on to high shower stays on but trips rcd doing rest of house , bear in mind we done the work half a year ago , all circuits are connected correctly with neutrals in appropriate bars ,
head scratcher
 
Tightened every connection in board , at shower and pullcord

- - - Updated - - -

It does it everytime , I even switched every breaker off except shower and it still does it
 
but it's been fine for 6 months, so either there's a weird fault developed, or someone's been having a go.
 
Yeah seriously weird I done job in September , done full test before board change then rcd tests after , its a Hager board
if it was a crossed neutral or something obvious it would have done it at home time in September
 
grasping at straws here, but could the shower have developed a leak, perhaps from the waste, and is wetting another circuit, under the floor, maybe?
 
Have you done an IR test now and compared it to your EICR from when you fitted it? Also do a continuity test in-between both neutral bars just in case someone has tapped into a circuit since installed.
 
well if all things being equal , and no changes to the wiring.............

then the shower is still faulty no matter how many elements the repairman replaces.
;-)
 
This is a real vague shot in the dark...!!!!!!
Is the shower cable running tight alongside another connected to the other side of the board and inducing a current in that cable's Neutral???
Have you tried clamping each circuits Neutrals on the tripping side, when the shower is on max?


Clutching at straws here!
 
Ill try that , I went today for 20mins to double check my work basically to rule out it being my fault , although its been fine for 6 months so obviously a new fault but wanted to show face
 
Showers have two heating elements, when the second element kicks in that is when it trips so that is the fault. Check the internal connections of the shower before sending it back to the wholesalers.
 
I had a 16th ed board, where the lights were not protected by an RCD, but if you turned the lights on off quickly it tripped the RCD in the board (even tho they weren't connected to it).
Swapped the RCD (even tho it seemed ok)
Problem solved

i would try changing the RCD
 
We didn't supply the new shower only rewired , customer didn't want to change it , Triton guy been out to replace element

- - - Updated - - -

Did you find out why that happens
 
I had a 16th ed board, where the lights were not protected by an RCD, but if you turned the lights on off quickly it tripped the RCD in the board (even tho they weren't connected to it).
Swapped the RCD (even tho it seemed ok)
Problem solved

i would try changing the RCD

did you find out why that happend

- - - Updated - - -

The second element ?
 
I would check the offending rcd. It sounds to me that either the two poles are not making properly when switched on or a loose connection maybe on the ingoing side.
 
Could be spikes from the electronic control causing currents to flow through capacitive filters on for example a washing machine. Have they got a new washing machine etc recently. Best way to test this is to unplug all the appliances and see if fault goes away. Just disconnecting the live doesn't work as they have capacitors N-E too and there could be spikes on the neutral too. had this problem once where spikes from church SON lamps tripped RCD in adjacent house.....Hope this helps
 
I've come across a very similar fault, someone had done a board change and everything worked. Now and again, when the Rcd tripped it would trip both or only one, with a full test I found both ring mains interconnected across both rcds. Main reason I was called to site was because when an Rcd needed resetting you had to turn each CB off and both rcds. The install actually functioned fine most of the time, albeit not very safely.

In my 22 years experience I've found 95% of the time, the simplest and most obvious answer is usually the right one. I'd start with checking continuity between the 2 neutral bars with CBs off then with them on, with power off of course.
 
[FONT=&amp]This thread reminds me of a Sherlock Holmes quote,”When you have eliminated the impossible, whatever remains, however improbable, must be the truth?”[/FONT]

[FONT=&amp]Here are a few things to think about.[/FONT]

[FONT=&amp]a) Has anybody else worked on the consumer within the six months?[/FONT] [FONT=&amp]
b) If you perform an RCD test, does the RCD’s correspond with the circuits tested?[/FONT]
[FONT=&amp]c) Is the second RCD feed from the first RCD (non time delay)?[/FONT] [FONT=&amp]

I know they are long shots, but at least we can eliminate them from the list.[/FONT]
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
wtf
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
36
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
glasgospark,
Last reply from
BigSi,
Replies
36
Views
3,521

Advert

Back
Top