Out of topic but what's the reason why there's a voltage to earth in IT system? And what's the ideal voltage?
 
It depends on the leakage to earth in each leg. A bit of damp weather can play havoc.

When testing always make one leg you’re reference point and work from that. If more that one person works on a system agree with the others which leg you are going to use. Makes passing on information easier.
 
what i mean is.. if you have 450V measured line-line. why we can measure more or less 230V line to earth?..im still referring to an IT system.
 
I’m referring to IT.
If you have a fairly even leakage from all 3 phases you will get a fairly stable reading for phase to earth. Leakage is like a resistor between each phase and earth. So long as that resistance is equal then you will have phase to neutral equivalent.
 