no hot water.. getting live on white when isolated? Valve not letting heat into tank side of valve.. although messy other wiring seems fine.faulty mid position valve right?
 
If anything is live when it is isolated then it surely is not actually isolated? Do you mean you have switched off the isolator and the white is still live?
 
The valve should give priority to hot water so that side should be open sounds like the valve has stuck and is back feeding to the white

A Y plan uses a mid position valve, this gives a 60:40 split between DHW and CH when both have demand not DHW priority, a system using a diverter valve would give DHW priority.

Where would the valve back-feed from to cause these symptoms?
 
no hot water.. getting live on white when isolated? Valve not letting heat into tank side of valve.. although messy other wiring seems fine.faulty mid position valve right?

Have you confirmed that the programmer and cylinder stat are switching correctly?
 
A Y plan uses a mid position valve, this gives a 60:40 split between DHW and CH when both have demand not DHW priority, a system using a diverter valve would give DHW priority.

Where would the valve back-feed from to cause these symptoms?

Sorry wrong terminology,When there is no power to the valve it should still be open to the hot water side. If there is power on the white when it is disconnected this could be coming from the grey back through the switch in the valve.
 
If anything is live when it is isolated then it surely is not actually isolated? Do you mean you have switched off the isolator and the white is still live?

The white wire was disconnected from the wiring centre while testing as i wanted to rule out backfeed. Seems like there is a problem within the switch,no power to either white ot grey should result in valve opening for DHW only.
 
Sorry wrong terminology,When there is no power to the valve it should still be open to the hot water side. If there is power on the white when it is disconnected this could be coming from the grey back through the switch in the valve.

Surely for the grey to become connected to the white, the valve to be stuck at CH only and the white to be live when there is DHW demand microswitch 2 must be stuck on and microswitch one completely shorted between all three terminals?
 
Don’t deal with y plan systems often but Honeywell do 2 port valve with a white wire that is normally closed. Is it possible someone’s fitted the wrong head and your not being given all the information
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

bigspark17

Arms
-
Joined
Location
wales
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Y plan fault.........................
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
10

Thread Tags

Advert

Thread statistics

Created
bigspark17,
Last reply from
bigspark17,
Replies
10
Views
3,551

Advert

Back
Top