stv292
custumer hasn't got a lot of money, shall i arrange for dno to p.m.e at the cost of 175 plus vat or tt it. i know p.m.e is far surpierier just looking for opinions.
custumer hasn't got a lot of money, shall i arrange for dno to p.m.e at the cost of 175 plus vat or tt it. i know p.m.e is far surpierier just looking for opinions.
Just make certain the earth cable is as per the requirements for PME.Further to Lenny's comments, ....If your clients do decide on going the PME route and paying that totally extortionate charge at a later date, your earth electrode can still contribute to the overall earthing of this installation by leaving it connected to the MET. So in effect the TT'ing of this installation is not by any means a wasted exercise...
So since the property was built there has never been any kind of earth facility? No disrespect intended but I find that hard to believe plus surely whoever installed the shower should have spotted it?
I'd bet this job turns into a nightmare for you