Just a quick check, as getting sorted today. If submain swa is indeed fed from TNCS source in the office cu and then out to yurt and at that end a metal cu with 2-3 circuits power, interior lights and separately 2 x 20W L.E.D. exterior lights all with rcbo protection and earth from TNCS divorced there through a plastic enclosure or similar and then TT rod earth for the cu in yurt. Would I need a simple mcb for the swa sub main out to yurt, or would that require more ? as only time delayed rcd's I can get hold of locally are double pole main switch type ones which would be not really what I need.
 
The SWA is a distribution circuit on a TNCS supply.
The cable is installed in such a way that it is enclosed by an earthed metal covering that is suitable as a cpc. Therefore the regulations do not require any sort of RCD protection to this cable.
An MCB will be fine (of suitable rating).

It is very hard to find any time delayed RCDs for single phase that are not double pole 2 module breakers.
I think I have seen some mentioned but never used anything other than 2M DP.
 
The SWA is a distribution circuit on a TNCS supply.
The cable is installed in such a way that it is enclosed by an earthed metal covering that is suitable as a cpc. Therefore the regulations do not require any sort of RCD protection to this cable.
An MCB will be fine (of suitable rating).

It is very hard to find any time delayed RCDs for single phase that are not double pole 2 module breakers.
I think I have seen some mentioned but never used anything other than 2M DP.
Thanks so much for that really appreciate taking your time out. It was a grey area for me as things have kind of gone Rcd/rcbo crazy here with most I know in the trade locally & didn't want to get anything pear shaped on the start ! Thanks again such a help.
 

Reply to Yurt supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello i've recently just had a re wire done on a three bed semi house, Ive noticed a few things im not 100 percent on ive spoken to the firm that...
Replies
24
Views
5K
My question is not quite in the title. I've been asked to quote for the above. No extraneous conductive parts in garage, which I intend to supply...
Replies
16
Views
5K
Been asked to quote for a mates mum for a job after my holiday! and my niceic assessment (29th!!) Basically she is getting one of them large...
Replies
8
Views
1K
Hello everyone, I know this has come upquite often, I have gone back through the many threads relating tothis topic. The reason for wanting to...
Replies
26
Views
15K
GEOFF S
G
M
Hi, would appreciate some advice please, I'm not a sparks. I'm dealing with a refurb on a warehouse with three WCs and a total of 6 electric...
Replies
27
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock