Delboybully

I went to a job this afternoon to replace a couple of bathroom lights. Did a Zs before starting and got 66.3 Ohms. So I investigated further and found the Ze was 66 Ohms on a TNS system.

I phoned the DNO (UK Power Networks in Hertfordshire) to inform them of this. Firstly they asked me where I had done the Ze to which I said at the CU. They told me they wanted one done at the head. So they gave me permission to cut the seals to do a Ze at the head- this amazed me as I thought (officially anyway) they didnt allow us to cut seals and play with their toys. This permission was given on the phone- should I have refused or gone ahead?

Secondly they said it wasnt an emergency, and they would prioritise those without power first and couldnt guarantee to come out within four hours. Now when I have had this situation before (Ze too high) the DNO have always said it needs to be fixed within fours hours so I told the DNO this and also pointed out that there were no RCD's present. They said they would try. I havent heard from the customer so I dont know if they made it within the four hours, I will phone the customer tomorrow.

I am what you like to call a 5 week wonder, I have the 2391 and have been doing electrical work for about 2.5 years.

Are the DNO correct in not giving it a response time of four hours or should they have been out withing four hours
 
The problem is the DNO make there own rules they won't guarantee you a figure they will give you the best reading they can depending on the location. Well thats the attitude they gave me. Did you check all the connections were tight in the head whilst you had it open? And yes surprised they have you permission to cut the seals. They make up the rules as they go along.
 
I did give the terminals a quick nip up but they were tight, The earth was connected to the sheath by a bonding clamp and I didnt fancy touching that but the cable and the sheath didnt move
 
if it's attached with a BS951 clamp, DNO might say it's nothing to do with them- stick a rod in. then you'll have to get some RCD protection fittted.
 
so...is there an RCD here at the mo?..

if not then stick an upfront one in as a temporary measure....
 
I went to a job this afternoon to replace a couple of bathroom lights. Did a Zs before starting and got 66.3 Ohms. So I investigated further and found the Ze was 66 Ohms on a TNS system.

I phoned the DNO (UK Power Networks in Hertfordshire) to inform them of this. Firstly they asked me where I had done the Ze to which I said at the CU. They told me they wanted one done at the head. So they gave me permission to cut the seals to do a Ze at the head- this amazed me as I thought (officially anyway) they didnt allow us to cut seals and play with their toys. This permission was given on the phone- should I have refused or gone ahead?

Secondly they said it wasnt an emergency, and they would prioritise those without power first and couldnt guarantee to come out within four hours. Now when I have had this situation before (Ze too high) the DNO have always said it needs to be fixed within fours hours so I told the DNO this and also pointed out that there were no RCD's present. They said they would try. I havent heard from the customer so I dont know if they made it within the four hours, I will phone the customer tomorrow.

I am what you like to call a 5 week wonder, I have the 2391 and have been doing electrical work for about 2.5 years.

Are the DNO correct in not giving it a response time of four hours or should they have been out withing four hours
Why worry about 4 hours? it's not an emergency i.e. loss of power. Either make it a TT and or temp RCD if you satisfied with all your readings. Ring DNO back for an update.
 
DNO were coming out, they just couldnt say they would be out in 4 hours, previous times I have called them they have said they would be out in four hours. Maybe it is different this time because it was late on a saturday afternoon and not during normal weekday working hours (maybe because they dont want to pay the guys overtime?)

Teletrix, I have seen loads of TNS systems with bonding clamps for the earth connection, One DNO guy I spoke to said they were fine. If the DNO refuse to sort the connection, I will have to put in a rod and some RCD protection

I did offer to put in an upfront RCD but the client decided they didnt want to pay for that!
 
leave the rod...

as i said go look in the back of the van for an enclosure with din-rail..and an RCD as a temporary measure....
 
If you had 2 customers, one with ze issues and one with no power - which would YOU attend to first?

Can't see the DNO is at fault here
 
If you had 2 customers, one with ze issues and one with no power - which would YOU attend to first?

Can't see the DNO is at fault here

Well, I'm not sure....... The customer with Ze issue could face electrocution but the customer with lack of power is not earning me money. Tough call.
 
what i couldn`t understand here as well is the twaddle about some rods....

i`v already said what the best temp solution would be...
 
I think the 'twaddle' about rods was in response to teletrix's post that the DNO may do nothing if its a BS951 clamp, in which he suggested making it a TT with a rod and RCD
 
I think the 'twaddle' about rods was in response to teletrix's post that the DNO may do nothing if its a BS951 clamp, in which he suggested making it a TT with a rod and RCD
after the DNo come out you may find there will be an official distributers earthing arrangement provided....

not if they see a bloody rod they wont...

so do yourself a favour will you...and dont make a rod for your own back.....
 
Just a quick update. The DNO turned up about 8pm which is around 4 hours after I phoned them. The customer told me they fiddled with the 'stuff in the cupboard' and said we have got down to 3 Ohms and they will be alright and they will come back.

They came back this morning and swapped the head out- This needed doing anyway as the head was broken and you could touch the bottom of the fuse if it wasnt for the electrical tape that was wrapped around the fuse carrier. I did a quick Zs at a socket near their CU and it came back at 0.28. Interestingly enough they left the 951 clamp in postion
 