Ze and PFC
Hi everyone,
Electrical improver here, got my college and 2391 under my belt, starting the 2396 in a fortnight. Aiming for gold card in march.
Got a question for you all:
Having a run in with my supervisor at work about this and wondered if you could clear it up for me, the below is an email I sent him. Basically regarding PFC and Ze: he wants me to keep the loop and pfc readings together for certification per test so that he can 'calculate the supply voltage' IE: The L-N loop reading and PSCC, and L-E loop (Ze) and PEFC. However, as far as I’m concerned the pfc is the highest measured and the Ze is: earth conductor out and test between L&E (its about limiting shock risk by finding the lower earth fault return path). Sometimes the PEFC will be higher, sometimes the PSCC be, but you always put the highest (it's about confirming the breaking capacity of the protective device is sufficient, not this calculation which he likes to use).
“I keep laboring at this bloody point but I can't get it out of my head now it's there. I've attached two photos here of my testing from the recent rewire we did on Monday/Tuesday. It was a TNC-S system
The image labelled Ze shows the following results (tested between line and earth with main earth disconnected):
A) Earth Fault Loop: 0.28 Ohms
Ipf: 0.833 KA
The image labelled Ipf shows my the Ipf between line and neutral (all conductors reinstated):
B) Fault Loop: 0.21 Ohms
Ipf: 1.10 KA
The highlighted figures would be those going onto my certificate and the ones which you'd use for the ohms law calculation. However, if you take these results and try to check them against nominal voltage the result would be way off:
0.28 x 1100 = 308 volts
Obviously if you do your calculation for either A) or B) they both work out swimmingly:
A) 0.28 x 833 = 233.24
B) 0.21 x 1100 = 231
I'm doing my best not to beat the ---- out of a dead horse here, but am I being a moron? I just don't think multiplying Pfc with Ze works as a test against nominal voltage to determine if the results are valid!
Help me out.”
What do you all think about this? Ze is the Ze right and PFC is the highest of either PEFC/PSCC readings, not just the PEFC? And if I do put the PSCC reading, I don't then put the L-N loop reading, right? It seemed to miss the whole point of each test!
You record the Ze and the highest of either PEFC or PSCC as the PFC on the certificate.
If you wish to use that calculation as a way to check the figures then you would obviously use the corresponding fault current and loop impedance. But this is not this isn't part of the standard tests and does not get recorded on the certificate.
You may find that some certificates, depending on which software or blanks you use, may have places to record both PEFC and PSCC.
Unless you have long tails or supply cables I would expect them to be almost the same.
Things like contact resistance, methods of measurement and so on come to play, remember this is not a real fault current,it's based on the meter loading the supply with a fixed resistance and trying to scale the volt drop, usually over several measurements, you can also try low current and high current measurements.
I often make a note of measured voltage just to check it's where I think it should be.
As per the reply above, I can do 10 tests on the same item and get 10 different results, I can then go and get the other meter out of the van and do another 10 tests and end up with a totally different 10 readings again, its just figures on a piece of paper, as long as they look right its not critical what they read.
I did a loop test on a lighting circuit the other day, came back at 3 ohms+, I thought hmm that's not right, readjusted the crock on the earth and it came in at 2 ohms, gave the meter to someone else to hold, clamped the crock onto the screw a bit tighter with my hand and it then said 0.94. I thought that will do nicely Who knows how accurate that reading was, could have been 0.84 or 0.85 or 0.91 or maybe just over an ohm or any reading in-between. But it was obviously well below the max allowed so who cares.