Hi everyone,
Electrical improver here, got my college and 2391 under my belt, starting the 2396 in a fortnight. Aiming for gold card in march.
Got a question for you all:
Having a run in with my supervisor at work about this and wondered if you could clear it up for me, the below is an email I sent him. Basically regarding PFC and Ze: he wants me to keep the loop and pfc readings together for certification per test so that he can 'calculate the supply voltage' IE: The L-N loop reading and PSCC, and L-E loop (Ze) and PEFC. However, as far as I’m concerned the pfc is the highest measured and the Ze is: earth conductor out and test between L&E (its about limiting shock risk by finding the lower earth fault return path). Sometimes the PEFC will be higher, sometimes the PSCC be, but you always put the highest (it's about confirming the breaking capacity of the protective device is sufficient, not this calculation which he likes to use).
“I keep laboring at this bloody point but I can't get it out of my head now it's there. I've attached two photos here of my testing from the recent rewire we did on Monday/Tuesday. It was a TNC-S system
The image labelled Ze shows the following results (tested between line and earth with main earth disconnected):
A) Earth Fault Loop: 0.28 Ohms
Ipf: 0.833 KA
The image labelled Ipf shows my the Ipf between line and neutral (all conductors reinstated):
B) Fault Loop: 0.21 Ohms
Ipf: 1.10 KA
The highlighted figures would be those going onto my certificate and the ones which you'd use for the ohms law calculation. However, if you take these results and try to check them against nominal voltage the result would be way off:
0.28 x 1100 = 308 volts
Obviously if you do your calculation for either A) or B) they both work out swimmingly:
A) 0.28 x 833 = 233.24
B) 0.21 x 1100 = 231
I'm doing my best not to beat the ---- out of a dead horse here, but am I being a moron? I just don't think multiplying Pfc with Ze works as a test against nominal voltage to determine if the results are valid!
Help me out.”
What do you all think about this? Ze is the Ze right and PFC is the highest of either PEFC/PSCC readings, not just the PEFC? And if I do put the PSCC reading, I don't then put the L-N loop reading, right? It seemed to miss the whole point of each test!
Electrical improver here, got my college and 2391 under my belt, starting the 2396 in a fortnight. Aiming for gold card in march.
Got a question for you all:
Having a run in with my supervisor at work about this and wondered if you could clear it up for me, the below is an email I sent him. Basically regarding PFC and Ze: he wants me to keep the loop and pfc readings together for certification per test so that he can 'calculate the supply voltage' IE: The L-N loop reading and PSCC, and L-E loop (Ze) and PEFC. However, as far as I’m concerned the pfc is the highest measured and the Ze is: earth conductor out and test between L&E (its about limiting shock risk by finding the lower earth fault return path). Sometimes the PEFC will be higher, sometimes the PSCC be, but you always put the highest (it's about confirming the breaking capacity of the protective device is sufficient, not this calculation which he likes to use).
“I keep laboring at this bloody point but I can't get it out of my head now it's there. I've attached two photos here of my testing from the recent rewire we did on Monday/Tuesday. It was a TNC-S system
The image labelled Ze shows the following results (tested between line and earth with main earth disconnected):
A) Earth Fault Loop: 0.28 Ohms
Ipf: 0.833 KA
The image labelled Ipf shows my the Ipf between line and neutral (all conductors reinstated):
B) Fault Loop: 0.21 Ohms
Ipf: 1.10 KA
The highlighted figures would be those going onto my certificate and the ones which you'd use for the ohms law calculation. However, if you take these results and try to check them against nominal voltage the result would be way off:
0.28 x 1100 = 308 volts
Obviously if you do your calculation for either A) or B) they both work out swimmingly:
A) 0.28 x 833 = 233.24
B) 0.21 x 1100 = 231
I'm doing my best not to beat the ---- out of a dead horse here, but am I being a moron? I just don't think multiplying Pfc with Ze works as a test against nominal voltage to determine if the results are valid!
Help me out.”
What do you all think about this? Ze is the Ze right and PFC is the highest of either PEFC/PSCC readings, not just the PEFC? And if I do put the PSCC reading, I don't then put the L-N loop reading, right? It seemed to miss the whole point of each test!