I need a bit of guidance/help/clarification, please.
I've just wired a loft extension. 3 sockets on a radial, 3 spots and smoke alarm. These are fed from a 2way CU in
loft, previously installed a few years ago on a 2.5mm radial. Protected by 20A mcb at main board.
Done all the r1&r2, IR etc. all ok.
Went to take a Zs reading on the new socket radial, and meter (Fluke 1652) showed error 4 (error 4 is described in
manual as "Fault Voltage". So i went back to basics and checked that the supply to the CU in loft was ok. I done a Ze
at the main board, but meter keeps showing error 4. So i'm now thinking that the earth is suspect. The supply is TNS. I
get a voltage of approx 245v between live/earth and live neutral. I've also done an RCD test at socket in the loft and
that reads ok.
To test my meter i've taken zs readings at home in various places and get a reading everytime.
I'm borrowing another meter from brother inlaw tomorrow to test again, just to make sure its not my meter.
I did at one point manage to get a zs reading on a different socket in the house and a ze reading at the main board, but
cannot get it to repeat.
Just not sure if its my meter or the supply at fault. The guy did have an extension built at the front about a year ago
which is probably where the supply cable enters the property. If the cable is damaged, i just need to sure that it is
before i contact leccy board.
Any thoughts or further checks that could be done? any help appreciated.
Thanks
I need a bit of guidance/help/clarification, please.
I've just wired a loft extension. 3 sockets on a radial, 3 spots and smoke alarm. These are fed from a 2way CU in
loft, previously installed a few years ago on a 2.5mm radial. Protected by 20A mcb at main board.
Done all the r1&r2, IR etc. all ok.
Went to take a Zs reading on the new socket radial, and meter (Fluke 1652) showed error 4 (error 4 is described in
manual as "Fault Voltage". So i went back to basics and checked that the supply to the CU in loft was ok. I done a Ze
at the main board, but meter keeps showing error 4. So i'm now thinking that the earth is suspect. The supply is TNS. I
get a voltage of approx 245v between live/earth and live neutral. I've also done an RCD test at socket in the loft and
that reads ok.
To test my meter i've taken zs readings at home in various places and get a reading everytime.
I'm borrowing another meter from brother inlaw tomorrow to test again, just to make sure its not my meter.
I did at one point manage to get a zs reading on a different socket in the house and a ze reading at the main board, but
cannot get it to repeat.
Just not sure if its my meter or the supply at fault. The guy did have an extension built at the front about a year ago
which is probably where the supply cable enters the property. If the cable is damaged, i just need to sure that it is
before i contact leccy board.
Any thoughts or further checks that could be done? any help appreciated.