sw-electrical
Hi guys,
I need a bit of guidance/help/clarification, please.
I've just wired a loft extension. 3 sockets on a radial, 3 spots and smoke alarm. These are fed from a 2way CU in
loft, previously installed a few years ago on a 2.5mm radial. Protected by 20A mcb at main board.
Done all the r1&r2, IR etc. all ok.
Went to take a Zs reading on the new socket radial, and meter (Fluke 1652) showed error 4 (error 4 is described in
manual as "Fault Voltage". So i went back to basics and checked that the supply to the CU in loft was ok. I done a Ze
at the main board, but meter keeps showing error 4. So i'm now thinking that the earth is suspect. The supply is TNS. I
get a voltage of approx 245v between live/earth and live neutral. I've also done an RCD test at socket in the loft and
that reads ok.
To test my meter i've taken zs readings at home in various places and get a reading everytime.
I'm borrowing another meter from brother inlaw tomorrow to test again, just to make sure its not my meter.
I did at one point manage to get a zs reading on a different socket in the house and a ze reading at the main board, but
cannot get it to repeat.
Just not sure if its my meter or the supply at fault. The guy did have an extension built at the front about a year ago
which is probably where the supply cable enters the property. If the cable is damaged, i just need to sure that it is
before i contact leccy board.
Any thoughts or further checks that could be done? any help appreciated.
I think that you need to rule out that the meter is itself faulty. Have you tried Ze & Zs readings on another property? (try your own).
This is where id start as trying to get a Ze/Zs reading.Once youve done that, you know at the very least if the meter is ok. If it performs perfectly on your address (assuming you have no faults) then you can continue to the next stage.
Otherwise you may talk to a hundred sparkys, all giving you advice and you could get to the end investigating things only to discover that it was the meter in the first place. Thats what id do anyhow...
"if the seal is missing" (cough cough) on the incomer test it and rule out the main supply cable. Take it from there.
btw great info given by the op (for a change) well done.
I have done zs on my on property, but not ze. I'm fairly confident that my meter is ok - i have been using it regulary recently. I'm just thinking back to what i checked at the clients (or should i say how i checked it). I'm thinking that the std suppliers earth path reading is very high, and my meter is timing out before it actually gets a reading. However I will have another look tomorrow morning and do more tests with bro-law's meter.
it would show up as a reverse polarity at the DP switch Paul if that was the case......assuming of course that the tails into the meter were correct...
Do a Ze at the head before the meter and then do the same after the head at the board, see if it is different. If it is you've got a problem at the meter and not the supply cable as said above.
Paul.m has the quickest solution would be to test at the incomer, but you can only do that if there is no seal.
To be honest l come across this quite frequently. If the seal was (cough cough) broken then all you would have to do is inform the DNO (after youve done the test).
Here we go again Glenn lol......
We are not talking about reverse polarity. The op is picking up a voltage on his meter (mft) so not allowing him to proceed with a Zs due to the safety for the device and readings. Mine cuts out at 4V I think (need to check that Paul).
Anyway Glenn, logging off for a bit, I'm sure you will pop up when I get back on. See you tomorrow for a pint and a debate, no fighting this time though "n' all" :wink:
Ok, but whats your thinking
Good question.
Well, it clearly should be close to zero. If it's excessive, then I guess a supply cable fault would be indicated. Problem is, I don't have enough experience to say what level would be regarded as excessive. Anyone else know what a "normal" range of neutral to earth voltage would be on a TN-S system?
Edit: Really just seeing if there's anything else which will add to the overall picture.
Thinking it through further, an excessive N-E voltage might be caused by voltage drop in the supply neutral, perhaps caused by a raised neutral resistance combined with a high current in the supply cable (not necessarily just to the property in question).
Good question.
it depends on how far away from the reference point you are....the further away from the star point in this case (TN-S)...the higher the Ub (contact voltage) will be.....
Ok thanks guys, got another meter now, so will go back tomorrow and test more thoroughly. I'll keep you posted
be good to know the outcome.
sw-electrical,
GLENNSPARK,