Brain dead at the mo,a 100 amp bs1361 fuse max Zs is .030,so how come tncs supply allows max 0.35 & tns supply allows max .80,surely the main fuse must comply to max allowed Zs in bs7671,any thoughts cheers
Hey Cliffed BS1361 fuse @ 100amps has a max Zs of 0.36ohms for 5 seconds disconnection (0.29ohms using RoT)
I think the confussion comes from the fact that a TNC-S system has max Ze of 0.35ohms and as such how can it(BS1361) comply with a max Ze if the RoT is applied - ie 0.29ohms maximum and max Ze of 0.35ohms for TNCS and even without the RoT for a TNS system at max Ze of 0.8ohms...
The answer I believe has already been given, ie if the BS1361 is the main fuse it is out of the scope of BS7671 and its max Zs values come under ESQC Regs as its DNOs equipment with different criteria. If protecting sub-main cable though it would need to comply though.
Good question and cant see why its been ridiculed.
I think his terminology and attitude when asked to look up something himself have been ridiculed, but the original question hasn't.
Thxs for your explanation,maybe I didn't explain it fully & correctly but it's great to have it answered,& I also thought it was a good question cheers
Hanging in there, take a little bit of banter and niggling, shake it off and the answer(s) will come! Us crusties have gotta have some fun along the way ..... :D
Agree with Zebra on this
The guy had already looked up the info before discussing it on here...not really the typical lazy assed questioner we sometimes get is he? -
I'm guessing there are a number of members (all levels of exp) put off posting to this forum as they are tired of the all too often belligerent and unnecessary slating that goes on.
I know we experience a fair amount of banter on site (particularly multitrade) but that's usually of humorous intent.
Bit confused, not too sure what the question was?
It seems to be something about the max Zs for the OCPD being higher than that for the installation?
Can't actually see a problem with that myself?