The PSCC, on single phase is around 16,000amps, 3 phase 27,000amps.
That may be so. But my missus giving you the evil eye will guarantee to kill you faster and yet strangely more painfully.
Ok, but you only need a fraction of an amp to kill a human so that is not really relevant.
The potential difference is the key, the more you have the more current will flow through the same resistance.
Of course it is a bit more complex than that, as the cells breakdown resistance alters etc.
You’ve got to be doing something incredibly stupid to get your body across two phases. The most likely event is phase to earth which is possibly but not necessarily fatal.
I doubt there’s many of you can say “I’ve never had a belt”, most of you seem to be alive.
Where did you get those figures from?
For a fault of that magnitude you would have to be on the terminals of a 500KVA 11/.4KV transformer (4.5% impedance).
(Based on the infinite source method.)
as a follow up, in domestic breakers are rated at 6ka. in comerical/industrial mcbs are rated at 10ka.
Building supply:
There is a 415 volt supply into the building, 3 phases, 1 neutral and an earth. The 240v supply comes direct off one of the phases and feeds the sockets and lights. The other 2 phases are not used and end in the supply cupboard.
Hope that helps!
P.S. As for a quote, I have an electrician who I'm hoping can do the actual connecting to the board but I am just trying to save money on the thing I can do if possible. Thanks though!
In the first place your electrician needs to check that you are being supplied with 3 phase and 3 phase meter. It could be that the two unused Service cut-out fuses are empty and the premises at the moment being classified as a single phase supply. That is probably the case, as a 3 phase supply comes with a higher standing charge than a single phase supply.
At least you have the means available to upgrade to a 3 phase supply, but the DNO will have to come in and make the necessary upgrade.
Don't try making any assessments on your installation yourself get a qualified electrician (and i don't mean a electrical trainee DI) to make all the assessments and design an installation that conforms to current regulations that will suit your needs, that's a very important part of an electricians value, not just the actual installation itself value.
i offered to quote him yesterday. this king of job is right up my street. been doing too much domestic lately. sick of seeing T/E that 's a pain in the arse when cold.
All i can say Tel, is this so-called electrician that is willing to just make the connections to his DB sounds more like a DI or DIY Dave than an electrician to me. For a kick off he's going to need a 3 phase DB, he ain't gonna get very far with an existing single phase board is he!! lol!!
These are 120KA, things don't always go to plan.
There’s time yet Tel you haven’t retired.
That fuse is one of two I’ve had fail like that. The other was a TC200A feeding a PFC capacitor bank. That blew holes through the top and bottom caps but the ceramic barrel held.
I kept them for my black museum.