Yes it may but dependent on a few factors...
Size of enclosure
Ambient temperature
% loading of mcb's in respect to the rating
Most mcb's are calibrated at 30c so any temperature lower or higher will alter the service current it can deliver e.g.
A 63amp B or C curve Merlin C60H at 30c has a max service current of the mcb rating, the same mcb at 20c has a max service of 66.2amps.... if you say had a ambient enclosure temp of 50c then the same mcb would be only good for max service current of 54.2amps.
This is another one of those areas that yrs of dumming down the education system has seen disappear... this is another reason why domestic trained and any modern trained Electrician should really thing about doing advanced design courses before going onto the larger projects.
This is not usually a concern at domestic level as the demand rarely goes close to the service current of the devices for any real length of period.
PS Noted you are USA so you need to seek advice within your own region this is advice under UK regulations and standards so may differ.