Hi All, Know this has been mentioned 1000s of times but here goes.
Customer would like NEW CU. Currently 16mm T/E 8m Run from Meter to CU.No Gas Bond,6mm water
I would like to fit 60a fused isolator , 10mm earths to gas and water and re use T/E. Think the CPC on T/E
is 6 or 10mm. The Max demand is low. A Colleague has apparently done this '100s of times'. I think that to
comply I need to run a 16mm earth from meter to CU ?
Any advice please
 
Where do the bonding conductors terminate ? MET near the meter with the earthing conductor or in the CU earth bar ?
 
If the gas and water nead bonding then i would run 10mm from met the adabtic equation should give you the answer
 
Last edited:
Yes thanks Flanders , I was going to run 10mm for gas and water from met but do I NEED to pull in 16mm from met to cu ?
 
What's the earthing arrangement? Have you carried out the adiabatic equation?
 
Last edited by a moderator:
I would say ths 6mm is suitable to the supply ths db as you are not taking the bond from tbe db
Without any information as to the prospective fault current or Zs requirements of the final circuits fed from this submain?
 