HappyHippyDad

~
Arms
Supporter
Evening all,

I am about to fit a solar panel to my shed and am trying to decide which inverter to get.

It will occasionally run a 2000w mitre saw (perhaps 2-5 minutes once weekly), this will be the highest wattage appliance used.

I was planning on getting a 3000w pure sign wave inverter but the cheapest I can find is £199. A modified 3000w sine wave inverter for about £170 or a 2000w modified sine wave inverter for around £40.

My question is am I able to run a 2000w appliance on a 2000w inverter as the price difference is significant? All research points towards needed a higher wattage inverter than the total wattage to be used, but some first hand experience from you guys would be very useful?

I'm almost tempted to risk the £50 inverter to see what happens?
 
i'd be tempted to give the cheapo inverter a bash. if it works, fine, if not, then you can relegate it to the van for charging ipads and buy a bigger one for the saw.
 
Evening,what is powering the inverter? Have you got sufficient battery power,or are you detonating a thermo-nuclear device,directly above your football pitch sized shed? :cool3:
 
i'd be tempted to give the cheapo inverter a bash. if it works, fine, if not, then you can relegate it to the van for charging ipads and buy a bigger one for the saw.

Thinks you're probably right Tel.

Evening,what is powering the inverter? Have you got sufficient battery power,or are you detonating a thermo-nuclear device,directly above your football pitch sized shed? :cool3:

105Ah battery, I've done the maths and I'll be OK for a 'few' mins with the mitre saw.
 
Are you running any other loads or just the saw for 2-5 minutes each week?

If it's just the saw I'd strongly suggest you look at a portable 3KVA or 4KVA generator as an option.

A word of caution, inverters are generally rated as short term peak load in KVA which means a 2KVA inverter won't run a 2kW saw for reasons such as;

1. A 2 KVA inverter will only usually deliver around 1800watts and with a non-premium brand that's with a tail wind down a hill.
2. You haven't accommodated the motor starting current which on a 2kW motor could be as high as 15A and as long as 0.5 seconds in duration.
 
You'd better order up a few spare bottle of magic smoke for the inverter when you get it, as I'm pretty sure it'll start leaking out all over the shop when you try the saw.


b783996ae2f65d9df67c273a1e944546.jpg
 
Last edited by a moderator:
What is the peak current rating of the inverter and for how long?
if the continuous load is 2kW then there may be a margin for starting.
You would also need to check if the inverter has a soft start mode so that the inrush current is limited.
You should also check that the saw will handle a modified sinewave as this may also increase the power drawn as the motor struggles.
£40 for a 2kW inverter does sound cheap so do that supplier/manufacturer also do a 2.5kW or 3kW version that could also be risked?
 
Are you running any other loads or just the saw for 2-5 minutes each week?

If it's just the saw I'd strongly suggest you look at a portable 3KVA or 4KVA generator as an option.

A word of caution, inverters are generally rated as short term peak load in KVA which means a 2KVA inverter won't run a 2kW saw for reasons such as;

1. A 2 KVA inverter will only usually deliver around 1800watts and with a non-premium brand that's with a tail wind down a hill.
2. You haven't accommodated the motor starting current which on a 2kW motor could be as high as 15A and as long as 0.5 seconds in duration.

I expect I'll be running other loads on it Marvo, but not at the same time as the saw so peak use will be the saw 2000w for 2-5 mins. Realistically I expect it will get used for perhaps 20 times at 5 seconds each over a couple of mins (per week).

The whole idea is for me to have a play with solar panels so the generator isn't an option. If it doesn't work well I'll just return to the grid.

I 'believe' Peak rating for the inverter is 4000w so this 'may' be adequate for the saw... Or may not! I have emailed the supplier for the spec on peak rating.



What is the peak current rating of the inverter and for how long?
if the continuous load is 2kW then there may be a margin for starting.
You would also need to check if the inverter has a soft start mode so that the inrush current is limited.
You should also check that the saw will handle a modified sinewave as this may also increase the power drawn as the motor struggles.
£40 for a 2kW inverter does sound cheap so do that supplier/manufacturer also do a 2.5kW or 3kW version that could also be risked?

As above Richard, i 'think' the peak rating is 4000w which may or may not be acceptable for the saw.
It states it is soft start, but its from eBay!
It may or may not be OK with a modified sine wave, but how do you tell? Microwaves, battery chargers, fridges seem to have problems with MSW, but I have not seen power saws mentioned.
 
Ebay introduces risk, but as you have a specification it does not sound much worse than buying from anyone unknown.
A good soft start system with a peak of 4kW may well make it if the soft start can drop the starting current by a factor of about 3.
On a modified sine wave the motor will be effectively driven and then not driven twice a cycle and this will introduce the starting current each cycle but because there will be limited torque to overcome as the motor is already rotating this should not be extreme but may well increase the overall current drawn compared to a standard sine wave pattern.
But it would be dependent on the motor construction, I am expecting it is a capacitor start motor.
 
Am I missing something, how big is your shed and how many solar panels will you be using to attempt to generate 2kw? I have twelve decent 450w panels and a fronius inverter on a bright sunny day in the middle of Summer I may get somewhere near 4kw at a push. Today the Sun is shining and I am generating 450w, but on a bright note I am being paid about 45p for every KWh whether i use it or not. I have no confidence that a £50 inverter from ebay will do anything useful other than charge a few batteries as previously suggested:-)
 
A few notes:

There is a world of difference between expensive and cheap inverters. An 'expensive' 2kW unit made to a decent spec is around £1000, so the £300 one is cheap and the £50 one borderline impossible. Most high spec inverters I have seen / installed run through their expected service life without problems. Most of the cheap ones blow up within a year or two, usually either when presented with a large surge like starting a motor, or continuous load near their rating longer than their thermal time constant. They are never economically viable to repair.

'Modified Sine' is a 3-step waveform that is not in any way sinusoidal, however it is designed to have the same peak to RMS ratio as a sinusoid. This enables loads that are dependent on the RMS (e.g. filament lamps, universal motors) to run on the same voltage as those that are dependent on the peak (most electronics). If the saw has a universal (series brush) motor it should be OK, although if it also has electronic speed control that will probably object to the MS waveform and either not work or go bang. Induction motors used in professional quality saws will also usually run on MS but their starting current may be excessive and they often cause inverter destruction. The maximum running torque may be reduced. **Any cordless tool chargers with non-isolated battery outputs (typically older ones) are likely to go bang if connected to MS inverters as they are dependent on the waveform**

A 2kW saw will only consume 2kW when full loaded and most consumer / prosumer grade tools with universal motors would rapidly burn out on a continuous load equal to their nameplate rating. Running light may be 500W or less. Starting load might be x3 for a power tool so this is invariably going to be the limiting factor.

ELV cabling needs to be very thick and short for this kind of load. On 12V the volltage drop is (240/12)² = 400 times more critical than on 240V. For this application I would aim to use 25-35mm² no more than say 1m long. The greater the drop, the closer the inverter will be pushed to its primary current limit during starting.

In short you have chosen a particularly demanding test for your solar shed.
 
Last edited by a moderator:
Am I missing something, how big is your shed and how many solar panels will you be using to attempt to generate 2kw? I have twelve decent 450w panels and a fronius inverter on a bright sunny day in the middle of Summer I may get somewhere near 4kw at a push. Today the Sun is shining and I am generating 450w, but on a bright note I am being paid about 45p for every KWh whether i use it or not. I have no confidence that a £50 inverter from ebay will do anything useful other than charge a few batteries as previously suggested:-)

I think the intent is to not use power at all except on odd occasions, whilst there is no power use the batteries can be fully charged and can deliver the required power in a short burst when needed. The panels only need enough power to be able to fully charge the batteries over a week.
 
Am I missing something, how big is your shed and how many solar panels will you be using to attempt to generate 2kw? I have twelve decent 450w panels and a fronius inverter on a bright sunny day in the middle of Summer I may get somewhere near 4kw at a push. Today the Sun is shining and I am generating 450w, but on a bright note I am being paid about 45p for every KWh whether i use it or not. I have no confidence that a £50 inverter from ebay will do anything useful other than charge a few batteries as previously suggested:-)

I think the intent is to not use power at all except on odd occasions, whilst there is no power use the batteries can be fully charged and can deliver the required power in a short burst when needed. The panels only need enough power to be able to fully charge the batteries over a week.

Basically I want to be able to run 50w (approx) LED lighting for 2 hours p/day and a 2000w mitre saw for approx 3 mins (in a day - probably about once a week in reality)

Therefore that gives me 250wh power consumption (200wh x1.25(due to efficiency loses))

Battery capacity = [(wh x days of autonomy x 2 (50% discharge of battery)) / 12v]

= (250x3x2)/12 = 125AH battery required.

Solar panel required = watts required/no of direct sunlight hours

Therefore 250/2 = 125w solar panel.

20A charge controller and an inverter!!

I actually have a 175w solar panel and a 105AH battery which I think will be OK, but its all a bit of an experiment and a bit of fun:)
 
Last edited:
Basically I want to be able to run 50w (approx) LED lighting for 2 hours p/day and a 2000w mitre saw for approx 3 mins (in a day - probably about once a week in reality)

Therefore that gives me 250wh power consumption (200wh x1.25(due to efficiency loses))

Battery capacity = [(wh x days of autonomy x 2 (50% discharge of battery)) / 12v]

= (250x3x2)/12 = 125AH battery required.

Solar panel required = watts required/no of direct sunlight hours

Therefore 250/2 = 125w solar panel.

20A charge controller and an inverter!!

I actually have a 175w solar panel and a 105AH battery which I think will be OK, but its all a bit of an experiment and a bit of fun:)

You didn't mention a battery in your original post! Hence my comment, I now get it, thought you were going to try and run a power saw direct from your inverter as I am sure others did, on a sunny day I would be able to run a 2000w saw straight from the inverter, but then again it cost a lot more than £50!:-)
 
Last edited by a moderator: