Did an EICR opened the CU and found this burnt charred Neutral running downstream of the (main switch). What should I be looking for (other than a replacement tail)?
There were two or three C2 observations that may well have caused an overload - eg 5kW of water immersion wired into the ring final and the oven run off a 13a plug, but the live conductors looked OK.
Installation over 35 years old.
OC or very low IRs on all circuits.
R1+R2 ok as was Zs.
I know one answer would be a whole re-wire, but I want to know what caused this.
Thanks for any helpful replies

20170720_114228.jpg
 
That CU looks a right mess, I would be looking at the integrity of all connections paying particular attention to the N busbar, what a mess that is.
5KW on a RFC are you sure?
I foresee a CU change on the horizon. As well as some redirection of the RFC if that 5KW is correct, oh my.
 
The neutral connection is the sheaving degrading or it is the flash from the camera?

Nice amount of copper from the neutrals on show and the looped back live on the B6 breaker.
 
How have you come to the conclusion it may need rewiring.
 
From the pattern of heat distribution the neutral busbar terminal connection was loose or contaminated and the heat generated as the installation current passed through the resistance exacerbated the damage and increased the resistance and the heat and so on.
That connection should be good for over 100A so overload is an unlikely cause.
 
The neutral connection is the sheaving degrading or it is the flash from the camera?

Nice amount of copper from the neutrals on show and the looped back live on the B6 breaker.
Sheaving???
 
Has the insulation at the top of Neutral gone dry/brittle ,
can see where it's "flowed to blobs" .
RCD end doesn't look as tarnished !
(Nip it up - not completed?)
(or later diagnosis/messing about-RCD-tripping)
 
Where was the combustion on the plastic cu?
Loose neutrals and all that
Plastic will often lump together due to its molecular make up when exposed to heat. The heat here was insufficient to cause thermal breakdown of the molecules and hence no gas is released which would be required to create ignition.
 
As an a by, should the owner be told not to use the installation, until rectified?
Plastic will often lump together due to its molecular make up when exposed to heat. The heat here was insufficient to cause thermal breakdown of the molecules and hence no gas is released which would be required to create ignition.