You are showing which is live and which is neutral. What you are NOT doing is using voltstick on its own to show which is live or neutral, it is a polarity check, not a test as such. It's easier than running long leads and having two people on the job. You are not checking what the voltage or ze is at that stage. Now about that red wine.
What about it? Cotes du Rhone Tesco £4 a bottle not bd really.
It seems everyone has got so excited by the use of a volt stick to check polarity on what is, at that point, a TNC supply that nobody has mentioned the other obvious issues in the picture.
A BS951 earth clamp to connect to the means of earthing?
Where is the cable gland for the outgoing SWA (assuming it is SWA as it goes underground)?
And what is behind the flap on that plastic-looking CU?
He checked the polarity with a neon tester? Very professional, those things are only good for stirring your tea and stabbing holes in plasterboard walls...
Lucky he had that. Last one I had out on a job to install a DP Supply Isolator asked to borrow my tester because he had forgotten his. I was gob smacked.
Don't think anything wrong in using clamp on earth rod, it's not on the supply cable, and it certainly won't cause any crush damage. Using clamps on a lead sheath cable is a bit no no. Oour policy was if you came to a job and it had a clamp on the sheath, provided it was sound, no visible damage and ze ok then leave in situ. We had to use the tape and mesh type for the last few years I was working. I have seen some badly damaged cable by the old clamps, lots of them very loose, and the result of them going bang! We would not go looking for them, too many to change, same as metal clad cut outs, which changed if we find them. Still got some 30 amp rewireable cut outs up here, even some with fuses in live and neutral. To change any of them it's a make the service dead job, can't be worked on live.
You saying you can only use amendment 3 on domestic?
No, but I wouldn't have thought a metal unit in what looks like it has the potential to be a damp location was the best choice.
Something more corrosion resistant would have been better in my opinion.
They aren't really designed for this application, and most earth rods are smaller than the minimum diameter pipe that the earth clamp is suitable for.
What is the Ra of the earth electrode? Will the clamp handle the PFC?
Percyprod,
stevels4,
