Good one Pete.
I gave up a long time back
I gave up a long time back
Sorry but I'm still struggling to understand the question. There will be a Ze at the intake, and a Zdb at each sub board. The maximum permitted Zs at each DB will depend on the OCPD protecting the distribution circuit.Confusing hahahaha I’m only an apprentice so still trying to learn, there’s a Main DB which feeds another DB say DB1 which has a main switch that feeds a another DB say DB2, there’s a shedule of circuit details and results for DB1 to DB2 which I’ve measured the Zsb and ka at each one but confused will my Maximum earth loop impedance be the same as Zsb as it’s only the sub cable feeding the DB2 as no dead testing involved
Are you carrying out an EICR or are you looking at a Report done by someone else.
Yes I’ve got Zdb and ka, but I’m on about max Zs left hand side of RCD X1Sorry but I'm still struggling to understand the question. There will be a Ze at the intake, and a Zdb at each sub board. The maximum permitted Zs at each DB will depend on the OCPD protecting the distribution circuit.

It’s last years test report hence why I’m trying to find out why there is a Zs reading with no final circuits? And it’s 1 triple pole switch I presumeWhat is circuit 1TP?.....whatever it is, you want the measured Zs for it.
Not much more testing carried out...IR, for starters.
Read the circuit details.....the other sheet.It’s last years test report hence why I’m trying to find out why there is a Zs reading with no final circuits? And it’s 1 triple pole switch I presume
Says shore isolatorRead the circuit details.....the other sheet.