Are you carrying out an EICR or are you looking at a Report done by someone else.
 
Confusing hahahaha I’m only an apprentice so still trying to learn, there’s a Main DB which feeds another DB say DB1 which has a main switch that feeds a another DB say DB2, there’s a shedule of circuit details and results for DB1 to DB2 which I’ve measured the Zsb and ka at each one but confused will my Maximum earth loop impedance be the same as Zsb as it’s only the sub cable feeding the DB2 as no dead testing involved
Sorry but I'm still struggling to understand the question. There will be a Ze at the intake, and a Zdb at each sub board. The maximum permitted Zs at each DB will depend on the OCPD protecting the distribution circuit.
 
What is circuit 1TP?.....whatever it is, you want the measured Zs for it.
Not much more testing carried out...IR, for starters.
 
What is circuit 1TP?.....whatever it is, you want the measured Zs for it.
Not much more testing carried out...IR, for starters.
It’s last years test report hence why I’m trying to find out why there is a Zs reading with no final circuits? And it’s 1 triple pole switch I presume
 
It can't be far away, judging from the Zdb and Zs.
and if it's 3 phase, it's badly put together.
edit. Gone....you can but try.
 
It's not a final circuit then, it's a distribution circuit, and the schedule is specific for the distribution circuit. The final circuits will be connected to whatever DB it feeds, and there will be another schedule for those.
 