Afternoon all,

Just trying to clear something up, going through regs book at present.

Basically have got a TNC-S/PME installation, 16mm tails, 60/80a main fuse (think it is 60A), 6mm bonding to water and 6mm coming from service head to block then into CU as main earth.

Am I right that being as it is PME I am obliged to upgrade bonding to 10mm as per table 54.8 and that the note about bonding must be not less than half size of CSA for main earth only applies to conditions other than PME.

Just wanted to be clear as that's how I'm reading it, the job is a mains change. Thanks in advance.
 
No you are not obliged to do this unless you do the adiabatic equation and the 6 MM is not suitable.
If it's under 6mm then you are obliged to increase to 10mm for bonding and 16 mm for main earthing.
 
Minimum size is 10.0. People will state that 6.0 at one time was acceptable but you will not find this in a copy of the Regulations. The 15th Ed quoted you should consult your supplier with regards to minimum sizing so the chances of knowing whether your 6.0 conductors were acceptable at the time of installation is zero.
 
With TNCS the 10mm minimum is the norm ........... TNS 6mm can be acceptable

Tin hat on.

What you need to be aware of is that lots of houses don't have any bonding at all.
 
So when BS7671 refers to main protective bonding conductors it is referring to bonding of services? If so table 54.8 says minimum 10mm.

Up until this point if I have done a mains change and there's a set up of 60a fuse, 16mm tails and 10mm earth and 6mm bonding I haven't upgraded bonding (depending on circumstances) and have had a job like this looked at on an NIC annual visit, but this particular job has now had solar panels and it is the governing body of the solar company asking for the 10mm bonding. Will be tricky getting 10mm to the water under the sink so that's why I'm trying to be 100% clear.

Thankyou all for your replies
 
Proving the existing 6.0 is or ever was adequate will not be possible.
 
Isn't the size of a protective conductor either determined or selected, whereas a main protective bonding conductor, is selected from table 54.8, where PME conditions apply?
 