you cant get level 3 without experience in fault finding.
ik we had an exam but the teaching was so little, we did short circuit and open circuits, the problems were like loose cable, need to replace cables etc.. idk about water spillages
 
Water or tea in a socket is very unlikely to be able to cause enough fault current to blow a fuse or trip an mcb, but could easily trip an rcd.
If nothing has tripped Something else must have happened to cause another fault that has resulted in an open circuit on one or more of the circuit conductors probably at or before the first non working socket.
 
From your profile you say you have a level 3 C&G 2365, I think. Not withstanding you may be in training, you seem to have little grasp of things (with regards your problem), an I'm not trying to be belittling?
 
Water or tea in a socket is very unlikely to be able to cause enough fault current to blow a fuse or trip an mcb, but could easily trip an rcd.
If nothing has tripped Something else must have happened to cause another fault that has resulted in an open circuit on one or more of the circuit conductors probably at or before the first non working socket.
Has the OP actually tried resetting the rcd? sometimes they trip but the switch sometime doesn't indicate a trip, worth physically operating the switch to see if it resets, just saying.
 
Really looking forward to the outcome. Hes definatly not seeing a tripped RCD somewhere. Could be an older MCB board with external RCD fitted for the socoket outlets after a old EICR behind a load of coats in his cupboard
 