- Reaction score
- 25,606
Okay I have removed and tidied up some of the posts. Can we try and be respectful to one another and keep the thread on track. Thank you.
Discuss Sub main advice please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
You could put a Henley block in and split the tails like you suggested, but there should be 1 point of isolation for the whole installation,
Isolator? you will need an OCPD for the circuit, why 16mm2? did you calculate the load required? I bet that is overkill, also why a joint in a new cable run? have you got test equipment? there are plenty of other answers needed to the questions already asked to be fair.
Really ............ reg number please?
Nah... I was going to suggest a 10a light switch!! LolWhy an isolator? It needs an OCPD not just a switch.
Bbb p121What book is that in mossep?
Thanks, wasn’t taking the pi$$ I’m still on the byb and couldn’t find it...Bbb p121
Its in the BYB too, not sure what page though but probably a similar reg number.
Thanks spoon I’ll be in there later.537.1.4 A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation.
A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt both live conductors of a single-phase supply.
BYB page 154
Thanks mossepIts in the BYB too, not sure what page though but probably a similar reg number.
Reply to Sub main advice please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net