Micro brewery... Brewing Vat has 2 elements, 9kW and 6kW. Done the calcs and each element will be fed with 6.0mm XLPE. no problem.My query is would it be safe and compliant to split the 2 elements across 2 phases in order to balance better. Can't see a reg.preventing this, but something nags about having 415V PD in what is essentially a single appliance.
 
I've done work on commercial kilns in the past and the elements are single phase. But there is usually a bank of elements, so they are split across the 3 phases to balance the loading. So potentially you have 415V PD within the kilns, I can't see how this scenario (in terms of install) is any different than yours. So long as it is clearly marked up with the correct warning signs and both phases isolate simultaneously.
 
Last edited:
Any 3 phase appliance has 415v PD. It doesn’t need anything extra in the way of insulation or protection than if they were 230.

If you get it done by Xmas do you get paid in brew?

There’s a joke somewhere about Tel organising a p**s up in a brewery... I’m sure it’ll be along any time now
 
I presume it will be wired back to a 3 phase board with a 2 pole breaker, so I can't see a problem. Put a 415v sticker on the micro brewery.
 
each element is single phase, with a 6.0mm flex. each will have it's own local isolator fed from a single phase 50A MCB. ( fixed load so overcurrent protection not necessary) so there's no way of isolating them simultaneously. the way the customer explained, he needs to have either one or both in use at any one time. from the posts so far, it appears that you all agree it's OK, but introelectrics has suggested simultaneous isolation. bit unsure about that.
 
each element is single phase, with a 6.0mm flex. each will have it's own local isolator fed from a single phase 50A MCB. ( fixed load so overcurrent protection not necessary) so there's no way of isolating them simultaneously. the way the customer explained, he needs to have either one or both in use at any one time. from the posts so far, it appears that you all agree it's OK, but introelectrics has suggested simultaneous isolation. bit unsure about that.
No problem so long as its marked up. The kilns I refer to are installed in such a way that its fully isolated when the doors are opened. My thinking being that a 3 phase rotary isolator installed at some point to isolate both supplies simultaneously would be good practice, should it be required?
 
both isolators will, be adjacent to each other and can be isolated simultaneously albeit he'll need to turn both off manually at the same time.
 
Don’t really know about current regs on the matter but I used to work on 3phase calorifiers where each element had its own phase. I reckon as long as the OCPD is interlocked and the manufacturer permits it then it should be ok
 
Unless there is a safety issue there is no need for linked circuit protection.
 
Don’t really know about current regs on the matter but I used to work on 3phase calorifiers where each element had its own phase. I reckon as long as the OCPD is interlocked and the manufacturer permits it then it should be ok