For a ring final circuit in 2.5mm T/E, a 32A protective device should be fitted.They are all on one ring circuit but sorry, it's actually 2.5 - twin and earth. MCB protecting it is 40amp
For a ring final circuit in 2.5mm T/E, a 32A protective device should be fitted.They are all on one ring circuit but sorry, it's actually 2.5 - twin and earth. MCB protecting it is 40amp
They are all on one ring circuit but sorry, it's actually 2.5 - twin and earth. MCB protecting it is 40amp
I get what you mean now. Presumably it is 2.5 to the sockets. Double check this to be sureThe basement has it's own circuit panel - the max load stated on the labelling in 40a. That's via SWA from the main house board (as it runs out of the house, around the building and back down into the basement). This feeds 4 external double sockets via 1.5mm cable.
What is this black magic that you speak of? 2.5 mm protected by a 40 amp breaker? the cable will melt before the breaker trips.This feeds 4 external double sockets via 1.5mm cable.
What is this black magic that you speak of? 2.5 mm protected by a 40 amp breaker? the cable will melt before the breaker trips.
If the basement supply cable is large enough, make a mini sub board where it enters the basement and have a circuit for basement outlets and one for the garage. Run a cable to the garage. To get away with a lower cable rating and breaker size, you make it all a power circuit in the garage by putting your light fitting on a lead and plug and situate it so it plugs into a power point instead of it's own switch (you just switch it via the power point). To take it a step further you can add a breaker or isolating switch where it enters the garage.
It all relies on the size of the cable that is feeding the basement.