They are all on one ring circuit but sorry, it's actually 2.5 - twin and earth. MCB protecting it is 40amp

As above mate. Hope you don't have a ring main using 2.5mm protected by a 40A breaker..
 
The basement has it's own circuit panel - the max load stated on the labelling in 40a. That's via SWA from the main house board (as it runs out of the house, around the building and back down into the basement). This feeds 4 external double sockets via 1.5mm cable.
I get what you mean now. Presumably it is 2.5 to the sockets. Double check this to be sure
 
This feeds 4 external double sockets via 1.5mm cable.
What is this black magic that you speak of? 2.5 mm protected by a 40 amp breaker? the cable will melt before the breaker trips.
If the basement supply cable is large enough, make a mini sub board where it enters the basement and have a circuit for basement outlets and one for the garage. Run a cable to the garage. To get away with a lower cable rating and breaker size, you make it all a power circuit in the garage by putting your light fitting on a lead and plug and situate it so it plugs into a power point instead of it's own switch (you just switch it via the power point). To take it a step further you can add a breaker or isolating switch where it enters the garage.
It all relies on the size of the cable that is feeding the basement.
 
What is this black magic that you speak of? 2.5 mm protected by a 40 amp breaker? the cable will melt before the breaker trips.
If the basement supply cable is large enough, make a mini sub board where it enters the basement and have a circuit for basement outlets and one for the garage. Run a cable to the garage. To get away with a lower cable rating and breaker size, you make it all a power circuit in the garage by putting your light fitting on a lead and plug and situate it so it plugs into a power point instead of it's own switch (you just switch it via the power point). To take it a step further you can add a breaker or isolating switch where it enters the garage.
It all relies on the size of the cable that is feeding the basement.

An FCU feeding the light would be better than it being on a 13A plug.
 
edit: duplicate post
[automerge]1571729133[/automerge]
You may want to think again on the size of the cable for a 30M run. dependant on load that could be quite a volt drop. And total disconnection times ( loop impedance) will need checking to ensure the overcurrent device will disconnect in the required times in the event of a fault.
 