My towel heater used to go into a 13a fused switch, which then went into a junction box fixed inside a backbox on the wall.

Since re-fitting the bathroom, in order to move the towel radiator, I ran a 1 meter length of 1mm twin+earth cable behind the drywall from the junction box into the new location for the fused switch.

I have now plastered the walls, and suddenly worried is 1mm cable enough to carry 13a?
 
No as in how many watts?
Most come with a 1.0mm flex attached anyway but 1.0mm t&e for fixed wiring should be for lighting only.
 
But if it's only from the outgoing side of a switched fused spur [appropriately fused] and running a load of under 1 amp I think it would be ridiculous to use anything bigger.
 
Then why ever limit 1mm to lighting circuits if by the load, it’s all that’s needed?
Even appendix 15 has 1.5 minimum to a socket fused down via a fused spur,
 
That’s what table 52.3 states (also see note 4) preceded by regulation 524.1, for final circuits anyway.
As it’s not from a lighting circuit, 1mm shouldn’t be used.
OK, interesting, thanks, does that mean that any circuit that isn't lighting is defined as a power circuit? Surely if you've done the calcs and selected and appropriate ocpd for the cable thats what matters? Genuine question, ('tone' can be misinterpreted in print)
 