It's a good question. A scenario that should never occur, but it has.
@davesparks gives the correct answer, it simply needs digging out and the correct mechanical protection installed. However, the correct solution is not always possible, it would be a nice easy life if it was, although possibly a bit boring.
If the homeowner completely refuses to have the walls bashed about then I can't see any other option but to fit an upfront 30mA RCD. This could be fitted in place of the DP switch used in the switch fuse. An awful solution, but better than leaving the tails without protection.
I fit steel plates when they are hidden in walls, plus S type 100mA RCD up front in the switch fuse.