It depends on the type/size of the motor; at the larger sizes we would usually be given a starting characteristic - so 2.5xFLC up to 90% of the rated speed, then we would obtain the start time from the specific application - so a star-delta having 2.5x over a 10s run-up time. In this case I would ensure the protections do not operate, and set the hot and cold times such they don't trip on start up, be do operate before the hot and cold locked rotor times respectively.
On a star-delta starter you could get away with a type B, DOL on the other hand is usually 8x flc so you would need a minimum of C - when I design a motor circuit I would try to use a type D because that gives the best chance of starting without spurious trips, if this compromises the upstream protection then I would go to type C etc.
A motor circuit is no different to any other circuit - yes it has a high starting current - but so do many lighting circuits (although smaller overall ratings).
Beyond that it's just compliance with usual stuff such as isolation, achieving suitable Zs, cable ratings, voltage drop, harmonics and RFI and so on