Hi everyone,
A friend of mine has asked me to take a look at this vintage 60s lamp which is running a little hot on the 'HIGH' setting. It has a transformer in the main plastic body which converts the mains to 12VDC. There is a single positive wire running from the transformer through the metal shaft to the bulb (presumably via the ON (HIGH) - OFF - ON (LOW) selector switch on the main body but I can't get to this at the moment). The negative from the transformer is connected to the metal shaft which is continuous with the -ve of the bulb. The bulb is basically a 12v car bulb. The wattage on the bulb currently fitted is 21W 12V. The rating on the sticker on the lamp says 20W 12V.
The mains lead is in ok condition but has no earth and no outer sheath (as you can see in the picture - old skool!)
Couple of questions...
1. Is it safe to have the -ve from the DC output connected to the metal shaft?
2. Should the thing be earthed. If so then should I attach the earth from the mains to the metal shaft?
3. Why might it be running hot?
4. If I put in a lower wattage LED bulb instead of the filament bulb - as in maybe 5W instead of 21W - would that be bad for the transformer?
5. Should the mains lead be replaced with sheathed 2 core?
Cheers
Tom
It's not -ve. If it's a transformer then it's AC which doesn't have -ve and +ve - well yes it does, but they swap round 50 times a second.
It is fairly common to use that arrangement. I have a lamp somewhere with no wires between the transformer base and the adjustable lampholder - the arms are formed from two parallel bars, each of whcih forms one part of the circuit.
Depends. It could be double insulated - is there a DI symbol (square in a square) on it ? Any chance of a phot of the internals, and especially any labelling on the unit itself and the transformer.
Could be many reasons. It could be that it was designed like that. The transformer could be faulty (internal short between turns). Does it get hot if there is no bulb fitted ?
Probably not - but it may or may not work as intended, and it may create a lot of flicker.
If the LED bulb is designed to run from AC or DC or either polarity then it is likely to work. If it's designed for DC only and one polarity - then it may work the same on high and low, or only work on high.
Possibly, possibly not. The existing flex may, or may not, have double or reinforced insulation - if it does then it's OK, if it doesn't then it should be replaced.
And though it pains me to say it because those plugs are good quality, the likes of which it's hard to find these days - it'll have unsleeved L&N pins so it should be replaced.
Thanks so much for this. Gosh I must be tied - of course it wouldn't be DC as there is no rectifying circuit there. The transformer does look a bit old. The 3 position rotary HI-OFF-LOW selector switch feeds into the mains side of the transformer, adjusting the number of windings so I guess the output voltage varies accordingly. I have a decent multimeter and some decent insulated gloves so I guess it would be ok to measure the output voltage for high and low without the load..... what do you think?
I'll get you the photos and other info tomorrow if that's ok.
Cheers again
Tom
Hi again,
Just tested the voltages and we've got 15VAC on the HIGH setting and 10VAC on the LOW setting. Could this be an internal short on the transformer? The lamp casing does feel a little hot. Would a 12V rated LED bulb work okay at 15V. I am assuming that it will solve the problem of it getting too hot...?
There is no double insulation symbol on the labelling. It is a Lloyd lamp NA101
Cheers again.
The transformer is probably starting to fail and TBH it would probably be easier and quicker to remove all the existing electrical components and replace with DC LED and a suitable driver in the body.
Thanks for that. Any idea how long the transformer might last for? And if it fails, is that dangerous - i.e. fire - or will it just blow the bulb and trip a circuit breaker?
Ah, I'd read it as the switch was between one transformer wire and the bulb. I've seen setups where there's a diode in series in the low position so the bulb gets half-wave rectified DC on low, and the full AC on high.
As Strima says, probably easier to strip out the internals and convert it to a modern LED.
If the transformer is getting hot with no bulb installed, then it's likely there's shorted turns internally where the insulation has broken down. Over time, the heat will help the insulation degrade further and cause further faults. Eventually it could get very hot - remember that a 3A fuse will carry well over 3A without blowing, so probably at least 1kW of dissipated heat in the transformer before a fuse blows. it all depends on how it fails, it may fail with a short significant enough to just blow the fuse without going through the "melted blob" phase. Or there may be an internal thermal cutout - but you probably don't want to rely on that since there might not be, or it might not work, ...
Simon47's no-load test is a good one. Switch the mains on to high with no bulb in and check the temp after 30 mins. If the transformer remains cool - perhaps just barely warmer than when switched off - and does not buzz, it's probably 100% fine. Normally, when a small transformer has shorted turns it self-destructs fairly quickly in a cloud of smoke that smells of burnt varnish.
We don't know how hot it is getting. For comparison, we have 50W transformer-fed bench lamps here with the transformer in the base like yours. They run hot - 60° or so - it's uncomfortable to hold your hand on the base for long. They are designed like that for compactness; none of the transformers have ever failed.
What is its rated voltage? If it is 220V or lower, it will run hot on average UK mains. The more compactly a transformer of a given power rating is made, the closer to magnetic saturation its iron core runs. This makes it more sensitive to high incoming voltage and it will dissipate extra heat regardless of whether it has load.
Was the 15V measured with the lamp in circuit or not? If in circuit, that suggests the voltage is indeed wrong. If the lamp was removed, 15V off-load is a reasonable voltage to expect due to the poor regulation of small transformers.
Reducing the lamp wattage, and hence load current, will reduce the resistive loss in the windings and make it run cooler. This could mitigate high iron loss although it won't actually reduce the iron loss (if high incoming voltage is the cause). There will not be any harm to the transformer from the lower load.
Thanks again for the v helpful info. Actually the transformer feels quite cool - not overheating at all. Its the filament bulb and surrounding casing that feels a bit hotter than it should be and on the low setting it is not overly hot at all.
Thanks so much for this. Loads of useful info. The output voltage was tested without any load.
I haven't run it unloaded for more than about 10 mins but the transformer seemed pretty cool both unloaded and with the bulb in and I tried it with the bulb on HIGH setting for around 25 mins. The bulb plus surround was getting hot but the transformer (in the main housing) was nice and cool. It hums a little bit but not ridiculous.
As M-Ty noticed the bulb that it currently has is too high in terms of wattage. The lamp is designed to take a 13W (number 93) bulb. Mine has a 21W modern brake light in it.
The LED bulb you've found should work, since It will run from AC, but it will be a bit dimmer than the car bulb, and the brightness switch probably won't do anything.
Personally I would fit a filament car bulb of the correct wattage, and then the lamp retains its 'originality'.
Yes, it would certainly look better. Trying to source one now.
Good call Lucien! Just tested the voltage with the bulb in and it is 11.5V as oppsoed to 15V unloaded so it looks like the transformer is ok. Just trying the 30mins no-load test...
Hi again,
My friend wants me to replace the cable and the plug. Would it be ok to use 6amp rated 2-core cable like this: -
https://www.ebay.co.uk/itm/2-Core-F...146026&hash=item2a94bb19d4:g:9vgAAOSw7z1aAcuf
Or will the 6A max current be a problem. Not sure how much current a transformer (220V to 12V) like this would draw...
The fuse in the plug is 13A
On a technical note, the current taken by your lamp would be in the order of tenths of an amp (If that), so the flex you suggest would work. The 13A plug must have a 3A fuse in it.
On an ethical / legal note, if you are updating, hence modifying, the lamp, you are personally taking over responsibility for its safety. The lamp would have originally gone through a (hopefully) rigorous design and testing regime, and shown to be safe according to the standards of the time. By changing anything now, you invalidate that original verification. If it's your lamp, to be used by you, you might feel you are happy to take the risk of your own handiwork backfiring. But if its going to someone else, or be used by them, it's totally your responsibility to make sure what is done is safe (and prove it).
This really means technical competence and workmanship done to the proper standards, and then testing the updated item (eg PAT). Not knowing if "replacing the cable" involves screw terminals, or soldering, or modifying strain relief cos the flex is different, or if adding an earth will improve safety, it's impossible to advise.
Be sure to keep safe, and keep the lamp safe too!
I would temper that warning with my feeling that replacing the flex on a "like for like" basis, assuming that's practical (as you say, we don't know how the thing is constructed) would be "routine maintenance" rather than "modification". So the legal risk is much much lower - but you still need to be able to test it (especially IR since it has unearthed conductive parts).
I would be tempted to replace the flex with 3 core and earth the metalwork, upgrading it from a questionable Class II to a known Class I device - but again, that's without knowing how practical that would be as I've not seen anything but the two photos. I also have the means to test it, which I'm guessing the OP doesn't.
Hi again,
Thanks for all the help everyone.
Here's a short vid showing construction of the lamp - insides plus the wiring path.
It is mainly plastic but has the metal arm which is carrying part of the 12V supply to the lamp. There are 2 bolts attached to this and there is also a screw holding the base on.
There is also a retractable metal hanger which I forgot to mention in the first vid. I've shown it in this one...
The hanger is inside a plastic channel which is separate from the main compartment.
Should I earth the metal arm?
Cheers
Tom
Hi again,
Cheers
Tom
All credit to you Tadmeister for a thorough video. I just need to absorb the information!
Well done for that - I'm sure you'll get some suggestions!
Hi Tadmeister Tom
Just a few thoughts:
I guess the first task is to find some 3 core flex that will feed through the base! The strain relief bush you have is a type that I thought, once clipped on the flex, was supposed to push into the exit hole from the inside. But it doesn't look if there's room for that. I did wonder if some other original strain relief occupied that rebate where the wire comes out of the base.
If the bush you have is a type that clicks closed and stays closed (around a new flex) it should be OK to use. If you need another, Google is your friend.
I don't think it is practical or necessary to try to earth the sliding hanging bracket. It seems to have its own insulated pockets to sit in.
I suspect it is worth earthing the metal arm of the lamp, as it's connected to the secondary of the transformer to complete the circuit to the bulb. Opinions anyone? Transformer is providing isolated supply, presumably built with robust isolation pri to sec. But if transformer fails, earthing a good thing!
You need to somehow get a good connection to the arm, eg via a ring tag to the screw connecting to the transformer, or soldering to the existing tag. It's good practice to make the earth wire longer than the other mains connections, so that if the flex strain relief fails, and the cable were to pull out of the lamp, then the earth wire would be the last to disconnect/ break.
Looks like you are happy to do some soldering, so good luck with the restoration. If you can find someone with a Portable Appliance Tester, or equivalent test equipment, to check earth resistance and insulation resistance when you've finished that would be great.
Hi Tadmeister Tom
Thanks again for all your help. I can squeeze some 3 core 0.5mm 3 Amp flex cable through the aperture in the base. Do you think that'd be ok?
I've also got some 2 core 6amp flat cable which fits a bit better but I think the earthed option is probably safer.
I'm definitely ok to solder - I've built guitar pedals and a Fender valve amp in the past. I have quite a bit of experience in this area but don't have any formal electricians' training so I'm in the process of learning the various rules and regulations.
I don't have any PAT testing equipment but I have a decent multimeter. I could test the current going through the cable...
0.5mm flex is rated at 3A, so 'compatible' with a 3A fuse in the plug, though as we all know it takes a lot more than 3A to blow the fuse!
BS1363 the standard for plugs seems to say 0.5mm can be fused at 3A.
As suggested previously, the lamp is only going to take 1/10ths of an amp - it's fault current that's the issue. In practice I think your 3 core should be fine.
Thanks again. I think I can get the strain relief bush on the new cable but there is absolutely no room in the exit hole to wedge it in there so it will have to be just inside, stopping the cable from being pulled out (as it was with the old cable). However the fit is so tight with the 3-core that I don't think the cable would budge anyway.
Could I ask one more question? Inside the housing I would like to attach the new neutral wire to the end of the old neutral wire (which I have cut and you can see dangling in the vid). This is because the wire attaches to the rotary switch, which is right up inside the case, behind the transformer and so taking the old wire out completely and soldering the new one directly to the rotary switch is going to be a nightmare.
My plan was to splice (as in merge the strands) and solder the 2 wires together and apply 2 layers of heat shrink over the join. Is that the best way or is there an issue with the lasting insulation of heat shrink?
Cheers
Tom
Cheers
Tom
If you put the sleeving on the flex, make a mechanically sound joint and solder it soundly - i'm sure you know how to make a good joint, and then shrink two layers, I would judge that satisfactory. The alternative would be a crimp, but it's a fine gauge wire for that method.
Devon
60s lamp overheating
Tadmeister,
Tadmeister,