Hello People,

I have a 10kva site transformer with a 32a 2P+E plug with a 3G4mm2 H05VV-F(yellow) as input.

A temporary DB will feed him and a socket with the same characteristics will be provided but not sure if I still need to keep the same cable colour( DB is on 230v).

Thank you
 
Has it come supplied with the yellow cable and plug. Is it on hire.
 
Seems very odd it has a 110v plug. Personally I would check the rating plate and change the cable and hard wire it to a 40A breaker.
 
Seems very odd it has a 110v plug. Personally I would check the rating plate and change the cable and hard wire it to a 40A breaker.
Agree. Also I don't get this 110v plug. I was expecting to see a gland for input cable and that's it
 
Is there a rating plate or similar on it saying what the inputs and outputs are?

You might just have a 110V isolating transformer and not a 230V-110V step-down!
 
Is there a rating plate or similar on it saying what the inputs and outputs are?

You might just have a 110V isolating transformer and not a 230V-110V step-down!
Sorry for the late reply. The client bought a 6way 110v splitter box thinking to had a great deal(he actually got 2 at the price of 1). I have realised only when I went to see personally the unit!
 