10mm does seem like overkill. 6.0mm willl handle 45A, VD permitting.
so at 40A on 6mm at 50m you VD would be (7.8 x 40 x 50) = 15600mV or 15.6V. but will you need 40A (cannabis farm?)?
30A would be 11.7V - .sensible if you have LED lighting.
As stated its is for a a small chest freezer and the odd charger for drills ect
1 outdoor light and 1 batten style light I have answered the questions over and over
The 40A I measured up for was for over estimate in case later years I need anything else
I can not give any more information than what I already have
please only reply If its related not childish comments like above statement
Cannabis farm in a shed would be easy to find by local plod and a heat sensitive camera.
Same goes for normally cold roof space.
I think we were all a little surprised that you jumped 3 cable sizes after your first thoughts.
TBH, 2.5mm will probably be fine if it’s just a freezer, chargers and a couple of lights ONLY. Nothing else.
It was just the long run i was worried about with the 2.5mm
As for the cable jump
the original idea was a radial circuit coming form my CU in the house plus I totally different radial for hot tub so two different circuits both in 2.5mm
( I haven't done cals for hot tub yet)
Or
The cable jump (10mm) was to power a brand new CU in shed its self then form that board ( shed ) I would power the hot tub heat and shed
Thank you kevin