It's the run of 40m with bends and turns I calculate for 50m just incase10mm does seem like overkill. 6.0mm willl handle 45A, VD permitting.
so at 40A on 6mm at 50m you VD would be (7.8 x 40 x 50) = 15600mV or 15.6V. but will you need 40A (cannabis farm?)?
30A would be 11.7V - .sensible if you have LED lighting
As stated its is for a a small chest freezer and the odd charger for drills ectso at 40A on 6mm at 50m you VD would be (7.8 x 40 x 50) = 15600mV or 15.6V. but will you need 40A (cannabis farm?)?
30A would be 11.7V - .sensible if you have LED lighting.
Cannabis farm I was referring to budwonder what is childish about doing a volt drop calc.for you. also wonder if Amazon sell a sense of humour.
Cannabis farm I was referring to bud
It was just the long run i was worried about with the 2.5mmCannabis farm in a shed would be easy to find by local plod and a heat sensitive camera.
Same goes for normally cold roof space.
I think we were all a little surprised that you jumped 3 cable sizes after your first thoughts.
TBH, 2.5mm will probably be fine if it’s just a freezer, chargers and a couple of lights ONLY. Nothing else.