Well that is what I got taught by multiple instructors and tutors. an EICR you can put whatever limitations you want as long as you list them, you can omit entire circuits if you want, say you were doing an EICR for a flooded house, presuming the cu was well above the flood level, there is no point needing to test the upstairs sockets or lighting...
An EIC I was always taught should not have any limitations, although in the real world I agree its not always practicable, my point was putting LIM on all L-N makes it look like he just cant be bothered to do it or is testing like an EICR, where do you stop, LIM on L-CPC just incase. Cant be bothered to do R1+R2, might as well LIM that, and Zs cause you LIM R1+R2 would have to be done live, so might as well LIM that as well..
Different electricians fill out the forms differently and different electricians believe what they do is correct but think about it, in EICR's there is a part for limitations, this is not in an EIC. If limitations were allowed why would you not have the same part that is in an EICR to write limitations in an EIC?
Different assessors focus on different things. Mine last picked me up on not having fire rated clips on my conduit... In a plastic shed... When I pointed this out he was like "Oh um yeah well obviously here its ok but I meant just in general dont forget them."