HappyHippyDad
Supporter
Dec 18, 2011
5,378
6,731
405,788
Gloucestershire
I have just completed an EICR.
The earthing is TN-S. However, there is a BS951 clamp used for this. Is this acceptable? Did the DNO ever use this a BS951 as a means for clamping around the supply cable or would this always be DIY?
Ze is 0.23ohms, but that doesn't mean a great deal if the connection is not compliant.
Picture below, albeit a little poor. Ignore the bottom clamp, this is to gas. It is the clamp partially obscured by the meter tails.
Some did even though they aren't supposed to. Should be either a sweated connection or constant force spring (similar to that used on SWA joints), I'd C2 and a call to 105.
133.1.3 - clamp not appropriate for use.
Thanks Lister.
Reactions: Jim_e_Jib
If you do a lot of domestic work you will see loads and loads of pipe bonding clamps used to make a tns connection on the lead sheath
so common in fact that if the clamp looks in good condition and i get a decent Ze , then i don't even bother noting it anymore
I don't like it at all, personally. Although usually they will give a satisfactory resistance reading, there might only be small points of contact due to the low clamping force, I wouldn't trust it under fault current. If for any reason it penetrates the lead, it can start a fireball that stops only when the substation or feeder pillar fuse blows. Most unlikely, but avoidable, hence I would note it.
They should defintly not be used on lead sheathed cables, the lead will cold flow away from pressure causing the clamp to slacken. As lister says constant tension spring or a wipe. If you report it as high Ze it should be a priority job.
Definite 'No, no' for me.
I can't understand why anyone qualified or experienced would do it. It's not matter of the Ze, it could be putting others at risk.
It's bad on swa, too. Steel wire isn't solid.......and neither is the insulation being damaged.
That clamp is newish and the same make/age as the main gas bond clamp. So I'm assuming someone felt the need to 'upgrade' during a board change, the original earth was most likely bare etc.
Too many people misguidedly mess with the DNO cable sheath in this way, as Lucien points out there could be a massive fuse behind it - a single service cable can be jointed off a really big cable quite legitimately in line with supply regs so could well be an 800amp fuse or higher ! So in technical terms - bugger that ! ?
HappyHippyDad
Supporter
Gloucestershire
BS951 clamp used for TNS?
HappyHippyDad,
Dave OCD,