I have just completed an EICR.
The earthing is TN-S. However, there is a BS951 clamp used for this. Is this acceptable? Did the DNO ever use this a BS951 as a means for clamping around the supply cable or would this always be DIY?
Ze is 0.23ohms, but that doesn't mean a great deal if the connection is not compliant.
Picture below, albeit a little poor. Ignore the bottom clamp, this is to gas. It is the clamp partially obscured by the meter tails.

The earthing is TN-S. However, there is a BS951 clamp used for this. Is this acceptable? Did the DNO ever use this a BS951 as a means for clamping around the supply cable or would this always be DIY?
Ze is 0.23ohms, but that doesn't mean a great deal if the connection is not compliant.
Picture below, albeit a little poor. Ignore the bottom clamp, this is to gas. It is the clamp partially obscured by the meter tails.