It may be the integrated fan and lamp fitting is a safety electrical low voltage SELV type operating from a special separate safe mains to SELV 12V power supply.
Both the fan motor and lamp are energised from the same power supply. If this is the case then during the start and run up to speed of the motor the so called starting surge current will depress the output voltage of the power supply. Only when the motor is running at speed is the output voltage sufficiently back to normal 12volts for the halogen or led to draw enough current for them to illuminate. Both types of lamp also have there own short period when they draw more current than there rated running current. The delay in lighting the lamp is due then to the motor start up surge and then the surge period for the lamp.
Solution - separate SELV 12V supplies of suitable power for fan and lamp (preferred) or one more powerful regulated SELV power supply for both (may or may not eradicate delay). But then you would be modifying a bought product designed to be safe which opens up a minefield of safety issues.
Post details of the integrated fan and lamp.
ps: led lamps have minimum voltage requirements too.
Great suggestion, however the fan itself is actually 230v. Its only the light that is on a 12v driver. It’s not one of the built in ones
This is the same one on Screwfix
I wonder then whether it is a feature of the LED lamps you have used. In our home the mains voltage GU10 LEDs which do not have a dimmer switch use non-dimmable lamps and they come on straight away. In one room we have 12 dimmable GU10 LED lamps controlled by a Varilight dimmer switch. On turning on all are off, then the same one after a few seconds illuminates and then the remaining 11 all come on at the same time. It seems it is not one delay produced by the dimmer - it has a soft-start feature which one might expect would cause a delayed power up for all lamps. It seems this one lamp is the 'dominant' load upon first switch on. The dimmer was switched on at the 100% setting. At lower settings there does seem to be some individual lamp delayed illumination but this does not 'replicate' your situation of simple on/off control.
You might do a simple check on the lamps to see if they are dimmable and if so swap for a non-dimmable type.
Please check the LED driver specification to see if there is a minimum LED load requirement. And find out if it has a soft-start turn on feature.
I'd check too that the fan and the LED driver have been wired in parallel across the incoming mains L and N and not in series and then across the mains.
Will do thank you.
The driver I swapped it for just said 15w on it. I’m assuming it meant 15w max? As in it can power 0-15w.
I’ve just ordered one that specifically says 0-10w, so maybe this will work.
Next time I’m out I’ll grab myself a good quality non dimmable mr16 light to see if this cures it too.
My SO doesn’t mind the effect, it’s driving me mad. You’d think it would be the other way round ay
Just a quick one, my new driver arrived today, fitted and made no difference.
Once I got my glasses on, I did realise that the mr16 led bulbs I have are 12v AC, my driver of course is 12VDC. Would this make any/much difference?
Not that the lamp is ac. Some are dc which means one has to be careful which way they are plugged in to match the polarity of the supply.
It seems the delay is due to the driver - a soft start feature - intended to extend the life of LED lamps by not subjecting them instantaneously to the full supply voltage and current. You could confirm this by connecting the LED lamp across your car battery taking care of course not to short circuit the battery.
A conventional 230 - 12 Volts SELV transformer in lieu of the driver would probably light the lamp quickly. But you would have to purchase a SELV transformer suitably packaged for it be safe and suitable.
You might be better to delay the illumination of the other three so that they all turn on at the same time.
Are you a qualified electrician?
Thank you, I am yes. Is there something I can put in line with the other 3 Dow lights to delay them? Or shall I change them to 12v
If it was me....I'd make them all 12V same wattage, make, Part No so you only have to keep one type of spare lamp.
After some experimentation - you could try each lamp fed by their own but identical driver or all lamps fed by one driver- to determine if one or other arrangement produces all on together.
Or you could fit a DIN 'delay on' timer to the current group of 3 using one of these:
RS PRO SPDT Timer Relay, ON Delay, 24V ac 0.3 s → 30h, DIN Rail Mount | RS Components - https://uk.rs-online.com/web/p/timer-relays/8966810
Good idea about the delay on module, I could sort that. Although, obviously, I’d prefer to have them all instant as opposed to delayed
What do you think to using a standard 12v power supply? Such as the ones made by Puls, or similar
I actually have one of these kicking around in the garage, don’t ask me where from 😝
It seems most, if not all (that I can find) LED drivers have a built in soft start, so if I was the get a standard 12v power supply, issue solved?
It is worth a try.
Such DIN rail PSU need to be enclosed as they are not suitable for open use, and the cables going in/out would need to be restrained so connections not stressed, but if that fixes your problem then a matching DIN enclosure and a couple of cable glands might be your next step!
That psu is still switch mode so check it first as it may have a soft ramp up of its output which when powering all 4 LEDs may still cause some sequencing of illumination.
It is not declared as SELV which may be a problem if the shower ( is it for a shower? I cannot remember what you first wrote) led lamp fitting does not have a high enough IP rating.
That psi is still switch mode so check first there is not a soft ramp up of its output.
It is for a shower yeah. All the connections etc are in the loft. The light fitting itself is enclosed in a dedicated shower supply kit so I’m assuming it’s ip rated.
All I’d be doing is changing the driver to a power supply unit
Easy to test though and no real cost :)
The data sheet says it is:
Safe low voltage: SELV (EN60950, VDE0100/T.410), PELV (EN50178)
Prot. class/degree: Class I (EN60950) / IP20 (EN60529)
EDIT: Not the IP rating though, but in a suitable DIN enclosure should meet IP55 at least?
Please let us know how it works. As pc1966 has helpfully pointed out the psu you last mentioned meets the selv requirements.
What are The Safety Zones For Electricity In The Bathroom? | dmLights Blog - https://www.dmlights.com/blog/safety-zones-electricity-bathroom/#:~:text=If%20you%20still%20want%20to,Safety%20Extra%2DLow%20Voltage).
Please have a decko at the reference and the paragraph on Zone 0 about electrical equipment over a bath or shower.
It must be at least IPX7 and SELV as well. This refers to the lamp fitting and its connections and wiring to it since you will place the PSU well away.
The literature with the fan and lamp should tell you the IP rating of the light fitting.
brodders97,
brodders97,