Hello can anyone advise what they would do in this situation please. I have a wylex 100amp switch fuse that has an incoming and out going cpc connection which takes up to a 16 mm cpc. I have 16mm incoming and outgoing cpc, however how do I then earth the enclosure and the banjo as the cpc connection has no connection with the enclosure
 
I'm assuming you're working with a 3core or 5core swa and you're using 1 core as the earth?
 
Is it one of those where there are the earth terminals at the main switch isolated from the earth terminal on the back box.
 
I'm assuming you're working with a 3core or 5core swa and you're using 1 core as the earth?
Hi Toon yes a 3 core and one core as earth
 
Is it one of those where there are the earth terminals at the main switch isolated from the earth terminal on the back box.
Yes it isolated from enclosure
 
Similar to this one?


 
  • Like
Reactions: westward10
Similar to this one?


Exactly like that. Take the supply cpc to the back box terminal first along with the banjo cpc then another up to the switch body earth terminal.
 
Exactly like that. Take the supply cpc to the back box terminal first along with the banjo cpc then another up to the switch body earth terminal.
T e back box terminal is very small probably only 6 mm max
 
Exactly like that. Take the supply cpc to the back box terminal first along with the banjo cpc then another up to the switch body earth terminal.
Why don’t they just put in an earth block big enough
 
  • Agree
Reactions: pc1966
Hello can anyone advise what they would do in this situation please. I have a wylex 100amp switch fuse that has an incoming and out going cpc connection which takes up to a 16 mm cpc. I have 16mm incoming and outgoing cpc, however how do I then earth the enclosure and the banjo as the cpc connection has no connection with the enclosure
 

Attachments

  • FF8EEE30-9A68-4E7E-A4D8-AFA627336585.png
    FF8EEE30-9A68-4E7E-A4D8-AFA627336585.png
    974.3 KB · Views: 61
T e back box terminal is very small probably only 6 mm max
I noticed that in pictures of it. I really wonder why they have the switch CPC terminal at all, why not have just the box adequately sized?
 
It is a stupid design, being 100A I would have thought that terminal would take 16.0 have you tried it.
 
  • Like
Reactions: pc1966
Is it swa in and out or tails in.
 
Most of the spec online state that separate terminal will take a 16.0.
 
  • Like
Reactions: loz2754
I noticed that in pictures of it. I really wonder why they have the switch CPC terminal at all, why not have just the box adequately sized?
Yes exactly, I wonder how many people have installed one thinking the enclosure is linked to it
 
Most of the spec online state that separate terminal will take a 16.0.
No that’s the earth terminal joined to the switch , the three connection are L N E
 
Tails in swa out
Could you just take the 16mm CPC to a crimp lug bolted to the SWA's banjo and, assuming 3C SWA, also put a lug on the cable's SWA conductor to the same bolt?

i.e. Ignore the switch's through-CPC connection and the box's terminal strip completely.

EDIT: Also you could use a nylock nut if concerned about it coming loose.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Cpc connection wylex
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
59

Advert

Thread statistics

Created
Nigel sparks,
Last reply from
mattg4321,
Replies
59
Views
4,178

Advert